Buzz-light-bulb

Hello sparks

I am led to believe that doing a pssc and pefc, assuming that the values are same will determine it is a tncs, how accurate is this measurement as I've come across properties today with the dno supply head is in the property next door. Or do I test the resistance.
 
A measurement can give you a very good idea, if the two measurements are way out then it is TNS (or a badly connected TNCS!:shame:) if the measurements are close then it can be either way, a good TNS near other PME or the substation, or a normal TNCS.
Generally if the to earth measurement is higher than to neutral then you are probably TNS.
 
Assumption is the mother of all f&£k ups
Never assume nothing? If your test prove obscure you can always ask the dno
Then record appropriately
I'd hate to record a ze as Tncs or TNS if it wasn't when I had misinterpreted the supply
My apprentice would have a field day of mocking me lol
 
Why is the Head in a neighbouring property? If so ,it's incorrect. Where is the actual meter? Am I missing something?

Not common, but I see this sometimes with conversions; service head in the ground floor or basement and tails going up to a meter and D/B in the other flats. The problem then is isolating the supply to the premises.
 
have to agree with guitarist on this, for one measurement will not prove one way or the other, secondly i presume you are doing some sort of inspection therefore the connection to the means of earthing must also be next door and must be checked for security
 

Reply to tns or tncs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
559
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
993
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
933

Similar threads

Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K
  • Question
I think I might be tempted to test this theory, if it can be done without causing danger to anyone.
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top