I've got a TNS supply coming into the building with a reading of 0.76ohms. The maximum is 0.8ohms. On circuit one I have a 3phase socket with a reading of 0.88ohms on a breaker60898 C32, maximum permitted for this breaker is 0.72 ohms which is already below my reading of 0.76. How do I make this comply? (Please excuse any bad electrical terms as this is typed by Mrs. stumas at his request. :) He needs this information for what he is doing right now at work. Many thanks in advance)
 
change MCB for B type is 1 option. if he's doing a EICR, then a C3 code , unless circuit is RCD protected, then the max. Zs is 1667 ohms.
 
Why doesn't he ask his boss ? or is he the boss of his own company? Is this another pretender at work getting a forum to sort his problems for him, well shame on anyone who helps.
 
No. My husband is a very good electrician and an inspector and tester. He just wants to make sure he does it correctly. Tell me what this forum is for KAS1 if not for a little help when needed? Im sure my husband has helped people before as he has been thanked by the look of it by other people. Yes, I WILL stand up for my husband, as I think your comment is unfair. Thank you telectrix for your reply, I have texted him your reply. I have absolutely no idea what it means but I'm sure he does. :)
 
What is the cct wired in?

- - - Updated - - -

What is the installation method?

- - - Updated - - -

What is the air temp?

- - - Updated - - -

Where is he taking his measurements?

- - - Updated - - -

Is the readings calculated or measured?
 
Why hasn't he got his BGB with him?
I've got a TNS supply coming into the building with a reading of 0.76ohms. The maximum is 0.8ohms. On circuit one I have a 3phase socket with a reading of 0.88ohms on a breaker60898 C32, maximum permitted for this breaker is 0.72 ohms which is already below my reading of 0.76. How do I make this comply? (Please excuse any bad electrical terms as this is typed by Mrs. stumas at his request. :) He needs this information for what he is doing right now at work. Many thanks in advance)
 
It's depending on what that 3 phase socket is supplying as to whether you can change the MCB out for a type B or not.
If you can't, at this stage of the game your only option is to provide that outlet with an RCD device, and ask the client to contact the DNO as to the chances of a PME connection.


Before doing that, check that main earthing conductor for any loose connections, and confirm that Ze value by taking the earth connection directly from the cable sheath, rather than the conductor attached to the sheath. You (and the client) may just be lucky in finding the problem... lol!!
 
No. My husband is a very good electrician and an inspector and tester. He just wants to make sure he does it correctly. Tell me what this forum is for KAS1 if not for a little help when needed? Im sure my husband has helped people before as he has been thanked by the look of it by other people. Yes, I WILL stand up for my husband, as I think your comment is unfair. Thank you telectrix for your reply, I have texted him your reply. I have absolutely no idea what it means but I'm sure he does. :)

Doesn't sound like it. Probably a right cowboy :gunsmilie:
 
another solution might be to clamp the circuit and measure the current per phase. depending upon what the load is , you may find derating the breaker to 25A or even 20A is possible.
 

Reply to TNS supply reading query in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
564
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
998
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
938

Similar threads

I don't think I'd use it mate even the one line heading then one long paragraph screams ai. And untrustworthy. I don't think much has been edited...
    • Optimistic
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top