I've got a TNS supply coming into the building with a reading of 0.76ohms. The maximum is 0.8ohms. On circuit one I have a 3phase socket with a reading of 0.88ohms on a breaker60898 C32, maximum permitted for this breaker is 0.72 ohms which is already below my reading of 0.76. How do I make this comply? (Please excuse any bad electrical terms as this is typed by Mrs. stumas at his request. :) He needs this information for what he is doing right now at work. Many thanks in advance)
 
change MCB for B type is 1 option. if he's doing a EICR, then a C3 code , unless circuit is RCD protected, then the max. Zs is 1667 ohms.
 
Why doesn't he ask his boss ? or is he the boss of his own company? Is this another pretender at work getting a forum to sort his problems for him, well shame on anyone who helps.
 
No. My husband is a very good electrician and an inspector and tester. He just wants to make sure he does it correctly. Tell me what this forum is for KAS1 if not for a little help when needed? Im sure my husband has helped people before as he has been thanked by the look of it by other people. Yes, I WILL stand up for my husband, as I think your comment is unfair. Thank you telectrix for your reply, I have texted him your reply. I have absolutely no idea what it means but I'm sure he does. :)
 
What is the cct wired in?

- - - Updated - - -

What is the installation method?

- - - Updated - - -

What is the air temp?

- - - Updated - - -

Where is he taking his measurements?

- - - Updated - - -

Is the readings calculated or measured?
 
Why hasn't he got his BGB with him?
I've got a TNS supply coming into the building with a reading of 0.76ohms. The maximum is 0.8ohms. On circuit one I have a 3phase socket with a reading of 0.88ohms on a breaker60898 C32, maximum permitted for this breaker is 0.72 ohms which is already below my reading of 0.76. How do I make this comply? (Please excuse any bad electrical terms as this is typed by Mrs. stumas at his request. :) He needs this information for what he is doing right now at work. Many thanks in advance)
 
It's depending on what that 3 phase socket is supplying as to whether you can change the MCB out for a type B or not.
If you can't, at this stage of the game your only option is to provide that outlet with an RCD device, and ask the client to contact the DNO as to the chances of a PME connection.


Before doing that, check that main earthing conductor for any loose connections, and confirm that Ze value by taking the earth connection directly from the cable sheath, rather than the conductor attached to the sheath. You (and the client) may just be lucky in finding the problem... lol!!
 
No. My husband is a very good electrician and an inspector and tester. He just wants to make sure he does it correctly. Tell me what this forum is for KAS1 if not for a little help when needed? Im sure my husband has helped people before as he has been thanked by the look of it by other people. Yes, I WILL stand up for my husband, as I think your comment is unfair. Thank you telectrix for your reply, I have texted him your reply. I have absolutely no idea what it means but I'm sure he does. :)

Doesn't sound like it. Probably a right cowboy :gunsmilie:
 
that's what she said, mike. 0.8, 0.80.
 
another solution might be to clamp the circuit and measure the current per phase. depending upon what the load is , you may find derating the breaker to 25A or even 20A is possible.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
TNS supply reading query
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
13

Thread Tags

Advert

Thread statistics

Created
stumas,
Last reply from
telectrix,
Replies
13
Views
1,657

Advert

Back
Top