T

TimmyB

Hi all

A recent board change on TNS, found the Ze at 1.35ohm:( So made into TT but only getting 210ohm
thru rod. Board is all RCD so would it not be a better installation if we were allowed to use the TNS + the RCDs
After all we have the magic number of 1667ohm

cheers
 
Indeed but there is guidance that TT Ze should be below 200 but preferably around 100 (according to NICEIC).

Anything over 200 would be considered to be unstable.
 
Hi

The 1667 max applies to a circuit protected with a 30mA RCD, not the external Ze / Ra. If the maximum stated by the supplier is exceeded then contact them as it's their duty to maintain their earthing system.

Failing that you need an extra rod(s) to get your Ra reading down below the 200ohm mark.
 
The Supplier will say as its a TT sysytem it is th cuctomers earth rod not theres, In AScotland anyway the supply authority has no obligation to supply and earth.Probbably easier to drop in another rod.
 
I agree with what your saying about TT being the customers issue to resolve but as the original was TN-S and the Ze was over their given value of 0.8 then surely they should be contacted to try and rectify it??

9 times out of 10 they will just tell you to install a rod and convert to TT though.:(
 
Thanks for your replys

Yes i will hopefully imrove the Ra reading in this case

But do you not think that if the rules were different it would be a better
installation if we could use the TNS at a higher max value if all circuits are protected
by RCDs
 

Reply to TNS to TT for better or worse in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
949
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
706
Did a fuseboard change yesterday from an old wylex board to dual rcd on a TT system with 14ohms ZE and finished pretty late. Went back this...
Replies
0
Views
494

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top