Hi,

As I mentioned last night, I was going to be putting the earth rods in for this summer house this morning.

I put 8 rods in, this was one stack of two, and two stacks of three rods.

The readings from the two that were 3 rods deep were around 10 Ohms per location, and the two rod stack was approx 17 Ohms.

I tested the first rod at approx 10 Ohms, then connected the second rod to the first which was 17 Ohms which them reduced the total down to approx 6 Ohms, then connected the third rod which was 3 deep and that bought it down to 3.2 Ohms.

So the Ra that I achieved today was a respectable 3.2 Ohms

All rods were connected together with 16mm earth.

I am going to go back next week and bang in another couple of piles of two rods so another four in total because I want to get that sub 1 Ohm reading.

Anyway, what do you think, 3.2 is not bad is it!!


Reading from first rod: 10.6 Ohms (3x 4ft 5/8" Rods)
[ElectriciansForums.net] Todays Earth Rod Efforts

Reading from second rod: 17.2 Ohms (2x 4ft 5/8" Rods)
[ElectriciansForums.net] Todays Earth Rod Efforts

Reading from third rod: 9.6 Ohms (3x 4ft 5/8" Rods)
[ElectriciansForums.net] Todays Earth Rod Efforts

Reading from first and second rod combined: 6.3 Ohms
[ElectriciansForums.net] Todays Earth Rod Efforts

Reading from all three rods connected together: 3.2 Ohms
[ElectriciansForums.net] Todays Earth Rod Efforts
 
I could try putting another on the top of them, I could do with someone holding the rod so i can hold the hammer with two hands.[/QUOTE]


you tried something like this? might help

[video=youtube;0sLv4LLVPbA]https://www.youtube.com/watch?v=0sLv4LLVPbA[/video]
 
I'd need an SDS max bit wouldn't I? and I could rent a drill to do it, presumably an SDS max drill would do it or would I need something bigger?

thats fine, prob normal sds would do but might take longer, but vid below is sds max demolition hammer

[video=youtube;VJYhHZYu_4g]https://www.youtube.com/watch?v=VJYhHZYu_4g[/video]
 
I'd need an SDS max bit wouldn't I? and I could rent a drill to do it, presumably an SDS max drill would do it or would I need something bigger?

I got a cheap SDS Max from screwfix for a ton and bought a Bosch rod driver to go with it. The rod driver was bloody expensive but it has all paid for itself already. Only gripe is the last few TTs with crap Ra have all had PME upgrades available, so the kit is sat gathering dust!

I tried using an SDS plus to drive rods in; a lump hammer is better IMO. At least til your forearm starts to look like Popeye's that is.
 
I could try putting another on the top of them, I could do with someone holding the rod so i can hold the hammer with two hands.

or one of these :D much easier

[video=youtube;vvCZvNj8H30]https://www.youtube.com/watch?v=vvCZvNj8H30[/video][/QUOTE]
That seemed to go in easy.......Is that house built on a swamp?
 
And here's a Kango Model C doing the same thing in 1935. Of course in those days power tools were run direct from the mains without isolating transformers, and had metal cases and class 1 construction. So as the notice says on the side, it's important to earth the tool reliably (via the brown wire which was the proper colour then). But if the rod's not in yet...

I haven't driven any rods with my Model C but I have used it to dig up fence post footings and knock a wall down.

[ElectriciansForums.net] Todays Earth Rod Efforts[ElectriciansForums.net] Todays Earth Rod Efforts[ElectriciansForums.net] Todays Earth Rod Efforts[ElectriciansForums.net] Todays Earth Rod Efforts
 
I've got a similar looking Wolf,bit later vintage,and for some unknown reason,we always ended up using it for boring holes through crossing timbers and telegraph poles...no clutch and lots of motor inertia,so when it went self-aware,it did so for ages...

There is nothing like getting continued service,from vintage gear,i think it is why i started collecting anvils...and it's catching...my protege has just recond a 1948 Atco mower,with a kick-start Villiers,and mowed his sisters' lawn with it. :yes:
 
Interesting read, I wonder how many people would have been happy with a reading between 100-200 ohms...

Just out out of interest, how come you decided to tt the summer house?

I TT'd it for two reasons, one is that its a TNCS supply and taking it 70m down the garden in my opinion is not going to fall within what I would call extending the zone within a sensible distance that I would be happy with, plus to TT it, the cost involved in that is not that much different to an extra core of 16mm x 70m.

Inside the main house, everything should be at equal potential, but down the garden its a bit unknown, and stuff will be plugged in and taken into the garden too.

Think about it this way, if you loose your neutral in the suppliers TNCS supply, your exported / exntended earth to the summerhouse has just been lost / removed, then you are left with an earth that is going to act as a return neutral for the supply, so if you were touching a piece of class I equipment and loose the neutral, then you will become part of the circuit and get a shock (more than likely).

The customer is also looking at connecting a hot tub off the summerhouse, and feel it would probably be best to use a TT at the remote end due to the slim chance of loosing a neutral in the DNO TNCS supply as any metal work would rise to 230v, and as they have a number of class I fittings going into the summerhouse, like lights around the outside, and appliaces within, then I feel a low Ra with a nest of rods would be better. It would't take much to come into contact with true earth when stepping out a hot tub.

Who is paying for this experiment?

its not an experiment, yet I do feel like I am wanting to better the reading down to a very good figure at less than 1 ohm. The time spent on the earthing im not charging for as will be making enough out of the install of the summerhouse.
 

Reply to Todays Earth Rod Efforts in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
461
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
963
Hi Mainline and thanks for the reply. My inverter is only fed from the mains supply over a 4 hour period at night and it does not have any tie...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top