Hi,

As I mentioned last night, I was going to be putting the earth rods in for this summer house this morning.

I put 8 rods in, this was one stack of two, and two stacks of three rods.

The readings from the two that were 3 rods deep were around 10 Ohms per location, and the two rod stack was approx 17 Ohms.

I tested the first rod at approx 10 Ohms, then connected the second rod to the first which was 17 Ohms which them reduced the total down to approx 6 Ohms, then connected the third rod which was 3 deep and that bought it down to 3.2 Ohms.

So the Ra that I achieved today was a respectable 3.2 Ohms

All rods were connected together with 16mm earth.

I am going to go back next week and bang in another couple of piles of two rods so another four in total because I want to get that sub 1 Ohm reading.

Anyway, what do you think, 3.2 is not bad is it!!


Reading from first rod: 10.6 Ohms (3x 4ft 5/8" Rods)
[ElectriciansForums.net] Todays Earth Rod Efforts

Reading from second rod: 17.2 Ohms (2x 4ft 5/8" Rods)
[ElectriciansForums.net] Todays Earth Rod Efforts

Reading from third rod: 9.6 Ohms (3x 4ft 5/8" Rods)
[ElectriciansForums.net] Todays Earth Rod Efforts

Reading from first and second rod combined: 6.3 Ohms
[ElectriciansForums.net] Todays Earth Rod Efforts

Reading from all three rods connected together: 3.2 Ohms
[ElectriciansForums.net] Todays Earth Rod Efforts
 
It's an impressive result with so few rods. I'm guessing it's mostly clay?

I didn't mean to offend by calling it an experiment - it's just that you're exceeding the minimum requirements of BS7671, something that hardly anyone seems to do these days. I may have mistakenly got the impression you were just trying to see how low you could go on this particular job, rather than it being a contractual requirement.

In my experience, there's little chance of achieving reliable "TN" values, at a sensible cost, using driven rods (assuming correct spacing and buried interconnecting cable), so you must still rely on the RCD anyway.

Can you post up the measured Zs - it would be interesting to know how your Ra relates to the the overall loop impedance?
 
Hi,

As I mentioned last night, I was going to be putting the earth rods in for this summer house this morning.

I put 8 rods in, this was one stack of two, and two stacks of three rods.

The readings from the two that were 3 rods deep were around 10 Ohms per location, and the two rod stack was approx 17 Ohms.

I tested the first rod at approx 10 Ohms, then connected the second rod to the first which was 17 Ohms which them reduced the total down to approx 6 Ohms, then connected the third rod which was 3 deep and that bought it down to 3.2 Ohms.

So the Ra that I achieved today was a respectable 3.2 Ohms

All rods were connected together with 16mm earth.

I am going to go back next week and bang in another couple of piles of two rods so another four in total because I want to get that sub 1 Ohm reading.

Anyway, what do you think, 3.2 is not bad is it!!


Reading from first rod: 10.6 Ohms (3x 4ft 5/8" Rods)
View attachment 29132

Reading from second rod: 17.2 Ohms (2x 4ft 5/8" Rods)
View attachment 29134

Reading from third rod: 9.6 Ohms (3x 4ft 5/8" Rods)
View attachment 29133

Reading from first and second rod combined: 6.3 Ohms
View attachment 29135

Reading from all three rods connected together: 3.2 Ohms
View attachment 29131
Can I ask were they placed in a straight line and what distance apart thanks for sharing
 
This is a question that attracts many different answers.

General consensus seems to be minimum separation of 1x - 1.1x driven depth. If you can go twice that distance, there's certainly no harm in doing so.
 
Basically you only get "independent" Ra values to parallel if the rods are far apart, as they get closer together each rod is in its neighbours region of influence so the reduction in Ra from multiple rods gets less. This article has various formulae to allow estimation of those values:


If you have 2 rods and the separation is around the rod's length then you are getting about 80-90% of the improvement you would see if they were very far apart, and that is usually good enough.

Generally if you can get down deeper, below 1m or so, it is better as what is critical to low Ra values is moisture in the soil. The top layer often dries out during summer droughts or can freeze in winter, greatly reducing the effectivity of the top 0.5m or so.
 

Reply to Todays Earth Rod Efforts in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
461
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
963
Hi Mainline and thanks for the reply. My inverter is only fed from the mains supply over a 4 hour period at night and it does not have any tie...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

  • Borrowed earth
    If mechanily protected would a 2.5 not suffice.you could manufacture metal conduit just to get...
  • Duplicate posts
    Any suggestions for avoiding the duplicate posts that keep happening? I'm trying to delete mine...
  • Duplicate posts
    Any suggestions for avoiding the duplicate posts that keep happening? I'm trying to delete mine...
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top