I need to run some cables from the garage CU to a variety of points hither and indeed yon. As the upstairs of the garage will be used for accomodation there is rockwool 140mm insulation in the gable ends. My question is, can I use some oversized plastic conduit within the rockwool to run cables without having to worry about having to de-rate their capacity, or will I just have to surface mount?

Thanks for any replies

D2E
 
If the cable are installed in conduit within insulation the installation reference method would be method A. A de-rating factor would have to be applied. What size cable are to be used?
 
you only need to consider de-rating factors if the cable in question is covered by insulation for more than 0.5 metre according to 17th edition even if it's in conduit. Have a look at section 523.7 (cables in thermal insulation) of the regs.
 
you only need to consider de-rating factors if the cable in question is covered by insulation for more than 0.5 metre according to 17th edition even if it's in conduit. Have a look at section 523.7 (cables in thermal insulation) of the regs.
BS7671:2008 Amdt 1, has a table 52.2 which shows derating factors for various insulation lengths from 50mm to 400mm. From what I remember, the previous issue also had this (I don't have it to hand).
 
Hi,

I need to run some cables from the garage CU to a variety of points hither and indeed yon. As the upstairs of the garage will be used for accomodation there is rockwool 140mm insulation in the gable ends. My question is, can I use some oversized plastic conduit within the rockwool to run cables without having to worry about having to de-rate their capacity, or will I just have to surface mount?

Thanks for any replies

D2E

Table 52.2 for cable totally surrounded by insulation a length of between 100mm - 200mm derating factor 0.63
19.5 x 0.63 = 12.28 Amps

So your 1 light on a 6A breaker should be fine mate
 

Reply to Todays silly question in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
776
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
789

Similar threads

And if it's a garage then use metal clad accessories.
Replies
5
Views
409
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
769

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top