Hi Guys, looking for a bit of advice as I think I'm starting to confuse myself with this one!
We have just finished a new bathroom for a client and I was informed by the plumber everything would be piped in plastic. It turns out however, that the towel rail is on old pipes and he has no idea where they go or what they consist of.
All circuits in the bathroom are rcd protected, as far as I'm aware the main bonding is in place, a 10mm earth can be seen leaving the consumer unit and testing between the pipework at the boiler back to the met gives 0.02ohms. I'll try and locate the connections tomorrow. Everything else in the room is piped in plastic.
What at I can't understand is that testing the rail back to the met gives around 189ohms. I'd have thought if it were plastic, it would have been miles higher and if copper, then the same as the heating pipes around the boiler?
Having disconnected its electrical element, testing between the rail and the earth terminal on the shaver point and also to the shower give the same 189ohms so sub 1667 and in my mind fine. The rail is pretty much
Am I thinking about this the wrong way or does the rail in fact maybe need supplementary bonding?
All thought are appreciated!
Graeme
We have just finished a new bathroom for a client and I was informed by the plumber everything would be piped in plastic. It turns out however, that the towel rail is on old pipes and he has no idea where they go or what they consist of.
All circuits in the bathroom are rcd protected, as far as I'm aware the main bonding is in place, a 10mm earth can be seen leaving the consumer unit and testing between the pipework at the boiler back to the met gives 0.02ohms. I'll try and locate the connections tomorrow. Everything else in the room is piped in plastic.
What at I can't understand is that testing the rail back to the met gives around 189ohms. I'd have thought if it were plastic, it would have been miles higher and if copper, then the same as the heating pipes around the boiler?
Having disconnected its electrical element, testing between the rail and the earth terminal on the shaver point and also to the shower give the same 189ohms so sub 1667 and in my mind fine. The rail is pretty much
Am I thinking about this the wrong way or does the rail in fact maybe need supplementary bonding?
All thought are appreciated!
Graeme