This 4 pole MCB would obviously be fusing the neutral too, considering all 3 phases and the neutral would disconnect at the same time does anyone see a problem with this?
 
Have you calculated the pscc? Will 10kA cover it?

Know what your thinking here, but there are standard sized (just a bit fatter) MCB's (1/2/3 and 4 pole) with breaking capacities of 25+ KA Not sure if Hager do them mind!!!

Schneider, ABB, Siemens, are the manufactures that i'm thinking about...
 
I've already purchased a 100a 4 pole hager MCB, 15kA, only problem being its a 4 pole MCB so the neutral will be fused if used in one of the poles, anyone see this as a problem? If this breaker disconnects, all the phases will be out
 
I've already purchased a 100a 4 pole hager MCB, 15kA, only problem being its a 4 pole MCB so the neutral will be fused if used in one of the poles, anyone see this as a problem? If this breaker disconnects, all the phases will be out
What if the neutral disconnects first? Is a four pole a good idea?
 
Re: TP&N sub feed

I've already purchased a 100a 4 pole hager MCB, 15kA, only problem being its a 4 pole MCB so the neutral will be fused if used in one of the poles, anyone see this as a problem? If this breaker disconnects, all the phases will be out

Is this 4 pole MCB protecting the sub main your putting in then?

Discrimination between your final and supply circuits should mean that this MCB will only let go if you have a fault on the supply to your new board.

- - - Updated - - -

What if the neutral disconnects first? Is a four pole a good idea?


I'd like to see that :conehead:
 

Reply to TP&N sub feed in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
207
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
1K
  • Question
Nothing wrong with it. Which manufacturers have you got this information from? What do you mean by trip speed? Fuses and MCBs can operate in the...
Replies
11
Views
2K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top