I've already purchased a 100a 4 pole hager MCB, 15kA, only problem being its a 4 pole MCB so the neutral will be fused if used in one of the poles, anyone see this as a problem? If this breaker disconnects, all the phases will be out

If the neutral breaker element is clearly marked with an ''N'' or Neutral it will have compensated making and breaking. It may also just be an isolator (switch)... My advice would be to check with the manufacturer if uncertain on the functioning of the device you have purchased...



What if the neutral disconnects first? Is a four pole a good idea?

Highly unlikely, and if it did, then something would be very wrong anyway... lol!!!
 
If the neutral breaker element is clearly marked with an ''N'' or Neutral it will have compensated making and breaking. It may also just be an isolator (switch)... My advice would be to check with the manufacturer if uncertain on the functioning of the device you have purchased...

It is a 4 pole MCB with every pole fused exactly the same, there is no N or neutral markings on it..
 
Back to my post about the neutral possibly disconnecting before the phases in some types of isolators, some isolators are made so the neutral disconnects last but I'm unable to find the spec of them, just for interest really?
Any one know the rating and would be kind enough to help me out?
 
Gawd you're in a minefield with late break contacts. You'd also need the contact to be early make as well if it's for the neutral. I would stick with a device that's rated for isolation of a 3ph and N supply, a device with one of the poles designated specifically as neutral that way the make/break timings should be correct.
 
Yes, if it's designed as a 3ph +N isolator then the pole that's designated specifically as 'N' should be late break / early make. That said if it's a no-name or bargain basement brand I'd want to check the manufacturers specs myself, in fact if it was being used in a critical application I'd probably connect the supply and my data logger to the load side and check it for myself with the customers load off-line first.
 

Reply to TP&N sub feed in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
207
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
1K
  • Question
Nothing wrong with it. Which manufacturers have you got this information from? What do you mean by trip speed? Fuses and MCBs can operate in the...
Replies
11
Views
2K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top