James sparks

Hi all

Am looking for opinions on this one, I'll try and keep it brief.




Service cable comes in into a 3phase head (1361 100A). From the 3phase head to a Ryefield board. Single phase supplies (1361 60A) out of the Ryefield into single phase meters. SWA sub-mains from meters to flats.


Would you say the origin is TPN or SPN? The meters only offer a single phase supplies and the Ryefield etc is before the meter (so their property) but, it does enter/originate at a TPN service head.


Existing EIC has 60A 1-phase 2 wire as supply characteristics.

Is it a TPN supply/origin or becuase all of that is before the meter it's only a SPN that concerns us as the origin? There's no 3phase meter so there's no readily available TPN supply to use.



Thanks!
 
the building will be TPN but the flat will be SPN.
the flats will be spread over different phases the same as a house on an estate.

thats why its not uncommon to have every other house to have a powercut and not the lot
 

Reply to TPN or SPN in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
526
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
982
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
915

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
603
OK for a simple load. What happens with (say) SMPS LED drivers ? I'd guess : Loads aren't perfectly balanced, especially during startup, so one...
Replies
8
Views
740

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top