Hi all

Am looking for opinions on this one, I'll try and keep it brief.




Service cable comes in into a 3phase head (1361 100A). From the 3phase head to a Ryefield board. Single phase supplies (1361 60A) out of the Ryefield into single phase meters. SWA sub-mains from meters to flats.


Would you say the origin is TPN or SPN? The meters only offer a single phase supplies and the Ryefield etc is before the meter (so their property) but, it does enter/originate at a TPN service head.


Existing EIC has 60A 1-phase 2 wire as supply characteristics.

Is it a TPN supply/origin or becuase all of that is before the meter it's only a SPN that concerns us as the origin? There's no 3phase meter so there's no readily available TPN supply to use.



Thanks!
 
NICEIC tech helpline said the origin would be TPN & the primary over current protective devices the 100A 1361s.
 
the building will be TPN but the flat will be SPN.
the flats will be spread over different phases the same as a house on an estate.

thats why its not uncommon to have every other house to have a powercut and not the lot
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
TPN or SPN
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
7

Thread Tags

Tags Tags
None

Advert

Thread statistics

Created
James sparks,
Last reply from
shanky887614,
Replies
7
Views
6,863

Advert

Back
Top