Transformer rating; apparent power? | on ElectriciansForums
Discuss Transformer rating; apparent power? in the Talk Electrician area at ElectriciansForums.net
C
CPM
Hi
I've got a uni assigment which includes build an equivalent circuit.
The transformer is rated at 2.2kVA which I thought was the apparent power.
But if I calculate the apparent power by using Vp x Ip then I get 220VA.
To find the phase angle Im confused do I use the 2.2kVA or 220VA for the following
cos-1(realpower/apparent).
Help needed please.
Cheers
Well surely you are trying to find the PF no? which is True power/apparent power. As you say in your opening words the KVA is the rated power. What exactly is it you are trying to do? Anyway hope some industrial spark comes along and enlightens both of us on this.
Trying to find the phase angle of the no load current.
'Rated power' means the maximum power the TX can handle at rated voltage without overheating, i.e. under full load conditions. You are talking about a no-load test, so the rated power is unimportant here. The power you are interested in is the one you calculate from the Vp and Ip measured under no-load conditions, which I assume is the 220VA figure mentioned.
The rated power becomes relevant when deciding what current to apply for a short-circuit test.
Thats brilliant. Cheers for your help.
Now I've calculated Resistive and Inductive current. Core loss resistance and magnetising reactance.
Now for the short circuit test the Transformer Rated current is needed. How is that calculated?
Cheers
Reply to Transformer rating; apparent power? in the Talk Electrician area at ElectriciansForums.net
Yet another update: I believe what EDF have done is moved me from an Economy 9 to an Economy 7. I've just emailed them to ask if they can switch...
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...