Hi All,
So i was asked to look at at large 3 phase to 120V transformer around 85kVA - it was tripping the MCB instantly (it never used to)
I insulation resistance tested the primary windings to earth - >2000ohms
I continuity tested the windings and got 0.46 ohms per winding, they were all the same.
Thinking back it must have been internally star connected as only 3 connections out which explains the consistent reading.
What other tests should have been done and is the winding resistance low ?
The theory behind inductors is briefly coming back to me regarding chokes ect. that they would appear a dead short but due to inductance when energised so does that explain the low resistance?
my conclusion was the transformer is fine a but the MCB is at fault but they have a spare and it is fine with that plugged in.
Any advice regarding testing would be greatly appreciated to be honest I never really thought about it until i was asked to test one......
So i was asked to look at at large 3 phase to 120V transformer around 85kVA - it was tripping the MCB instantly (it never used to)
I insulation resistance tested the primary windings to earth - >2000ohms
I continuity tested the windings and got 0.46 ohms per winding, they were all the same.
Thinking back it must have been internally star connected as only 3 connections out which explains the consistent reading.
What other tests should have been done and is the winding resistance low ?
The theory behind inductors is briefly coming back to me regarding chokes ect. that they would appear a dead short but due to inductance when energised so does that explain the low resistance?
my conclusion was the transformer is fine a but the MCB is at fault but they have a spare and it is fine with that plugged in.
Any advice regarding testing would be greatly appreciated to be honest I never really thought about it until i was asked to test one......