Hi all,
I have a transformer with three 50va connections on secondary side , is ther any way i could run five 20watt downlighters from this, it is already in situ so if poss i weould use it , any thoughts??
 
All types of incandescent lamps, including GLS (general lighting service) lamps, incandescent reflector lamps and tungsten halogen lamps, have unity power factor, as they are purely resistive. Therefore, the connected load in VA of an incandescent lighting load is equal to the sum of the lamp watts.

Regards

Dichroic
 
I agree with electro, the tranny is rated at 150VA and you want to load 100VA, therefore ok. Make sure you use suitable size flex to supply the lamps, I would use 2 core 1.5mm, depending upon the length of runs.
Now, my only issue with this is when some muppet comes along in the future and replaces the 20W lamps with the the more readily available 50W lamps. The tranny will fry.
This is why I like to fit either 240V dichoric or energy saving downlighters, if the spec is 12V I fit individual trannys.
 
I personally agree with ghost, why unless stated do people still use transformers? Just something else to go wrong. 230V GU10 evertime, that way the only fault you can get is the lamps.


better light and less bulb trouble with 12v 50w halogen ,less severe on dimmers


the 230v gu-10 gives more options alright
 
I had to look into this a couple of years ago for a picky customer, and apparently the light output is 10-15% more from a 12v than a 240v, don`t know about the dimmer though.
And also the options on beam angles etc is better with 12v
 
Last edited:
I have never noticed a better light from low voltage lamps nor any difference in lifespan.
Why are they less severe on dimmers? I know some transformers offer a soft start feature, but in the long run they all draw the same current.


i imagine the inrush will be less severe with an electronic trafo than a gu10 halogen


i forget the detail after a while unfortunately


the mains lamps will be subject to overvoltage and surges more than the electronic 12v i think also
 

Reply to Transformer in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
594
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
949

Similar threads

  • Question
When I was at college doing the 2361 back in the 1980's I still recall to this day the instructor (Mr Wood) saying "Lads I do not want you to...
Replies
10
Views
656
Hi there, I have dismantled my DEFENDER POWER POD 3KVA 110V TRANSFORMER & upon re- connecting the wiring, there now appears to be 2 extra wires...
Replies
0
Views
168

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top