can anyone tell me what are the implictions of turning off the instantaneous earth settings of a transformer feeder.:hanged:
 
I think you first need to tell us Why, ...you want to turn this instantaneous earth setting off, for a transformer feeder breaker!! It sounds to me, that you have some sort of earth fault on this feeder??
 
Last edited by a moderator:
When you say ''Transformer Feeder'' what are you referring to the MV side or the LV side of things?? I'm assuming your talking about the LV side, but best to confirm.... lol!!

Come on tomnoel, What problems are you having with this feeder breaker, for you to want to negate the earth fault protection from this breaker???
 
When you say ''Transformer Feeder'' what are you referring to the MV side or the LV side of things?? I'm assuming your talking about the LV side, but best to confirm.... lol!!

Come on tomnoel, What problems are you having with this feeder breaker, for you to want to negate the earth fault protection from this breaker???

During recent testing our TX feeders tripped on inrush To over come this it has been suggested that we turn off the Instantaneous Earth Fault Setting on the TX feeders and still achieve grading with the UKPN relay at the max earth fault setting of 1.5KA. Any Comments.
 
During recent testing our TX feeders tripped on inrush To over come this it has been suggested that we turn off the Instantaneous Earth Fault Setting on the TX feeders and still achieve grading with the UKPN relay at the max earth fault setting of 1.5KA. Any Comments.

Can you give us a better breakdown of the system your talking about and it's age. A nice photo of the breaker(s) and it's electronic protection unit, along with any other protection relays you have on this circuit, would also help me to advise you. From what little you have stated, this sounds more of a bodge rather than a fix!! lol!! All Instantaneous protection elements, including earth fault settings also normally come with a time (delay) setting.... which would/should cover any inrush cycle. Not sure what your grading with/against, using the relay max earth fault setting.

I'll also ask again, are we talking about the MV side or the LV side?? I ask because i'm beginning to think your talking about the MV side of things, as TX feeders will be the main incomers on the LV side of things, and wouldn't see inrush... But sometimes terminology can be confusing!! lol!! By the way, who has advised/suggested turning off the instantaneous element of your earth fault protection???

Another thought, ...any chance of posting a very simple one line drawing showing the protection relay positions, hand drawn is fine!!
 
I can’t see how inrush is showing as earth fault, instantaneous overload maybe. As E54 has asked is this the MV or LV side that the fault is being detected. An incorrectly set restricted earth fault on the LV side is a possibility, but it’s a remote one.

Who has recommended disabling the earth fault, it’s not something you would do as a permanent fix. Can the time lag be adjusted?

One last question, is this a new fault or a long running sarga.
 
I can’t see how inrush is showing as earth fault, instantaneous overload maybe. As E54 has asked is this the MV or LV side that the fault is being detected. An incorrectly set restricted earth fault on the LV side is a possibility, but it’s a remote one.

Who has recommended disabling the earth fault, it’s not something you would do as a permanent fix. Can the time lag be adjusted?

One last question, is this a new fault or a long running sarga.


Much better put than i Tony, ...but then i'm in holiday mode!!! lol!!!

Some of the older TX,s that's been in service for a good many years, can have problems with EF during times of inrush, but generally nothing that can't be protected against, depending of course on what protection relays are incorporated in the system. Even R/E relays have a suitable time delay... lol!!
 

Reply to transformer in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Interesting. Sounds unusual since it seems it was very lightly loaded. Not much you can do I suppose other than buy a replacement unit. Unless...
Replies
7
Views
537
  • Question
One of those backlight Chinese testers may have helped that’s if the tester didn’t catch fire or electrocute you. LED TV Backlight Tester 12W LED...
2 3
Replies
68
Views
4K
  • Question
I would add that those MCB recommendations are for fault protection, not for overload protection of the transformer. It might have its own...
Replies
7
Views
1K
It sounds like there is either something up with the wiring to (or from) that thermostat, or the thermostat itself. If you disconnect all the...
Replies
3
Views
813
  • Question
Looks like the above is the current model of the whole unit - well done ElectroChem! If you don't fancy the 379 euro's of the Becker unit, you...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks