J
JulianC
Currently looking at a 99kWp system, using 6 x SMA TriPower 15000TL transformerless inverters. I've been digging into the requirements for the elusive type B RCD and have found a handy guide from SMA here:
http://download.sma.de/smaprosa/dateien/7418/RCD-UEN103120.pdf
Page 8/11 is interesting in that it states that "all SMA inverters with transformer and all transformerless SMA inverters mentioned in the following are not capable of feeding DC residual currents to the grid due to the circuit design" - it then proceeds to list the majority of SMA's transformerless inverters.
Compare this to 712.411.3.2.1.2 which states "Where the PV converter is, by construction, not able to feed d.c. fault currents into the electrical installation, an RCD of type B.....is not required"
Happy days!
http://download.sma.de/smaprosa/dateien/7418/RCD-UEN103120.pdf
Page 8/11 is interesting in that it states that "all SMA inverters with transformer and all transformerless SMA inverters mentioned in the following are not capable of feeding DC residual currents to the grid due to the circuit design" - it then proceeds to list the majority of SMA's transformerless inverters.
Compare this to 712.411.3.2.1.2 which states "Where the PV converter is, by construction, not able to feed d.c. fault currents into the electrical installation, an RCD of type B.....is not required"
Happy days!