R
redface
now i think i should know this but i don't know wether logic will apply
a 230 to 110V transformer
the 110V machines will take about 30A which is about 3.6kva
now the cable will run about 20m and i was going to run in 10mm 3core swa to a 40A switch then i was going to run a 4mm tw/e ring now this will run at 30A constant that is why i have used that size cable and it is very sensitive equipment so i don't want much volt drop at all do you think this is ok or well over the top ?
the other question is its 30A on 110V side so is that the same on 230V side or should it be protected by a 16A breaker?
am i right the lower the Voltage the higher the volt drop can any one show me a calculation for this to work it out please
redface
now the cable will run about 20m and i was going to run in 10mm 3core swa to a 40A switch then i was going to run a 4mm tw/e ring now this will run at 30A constant that is why i have used that size cable and it is very sensitive equipment so i don't want much volt drop at all do you think this is ok or well over the top ? If you are aiming for low volt drop then the bigger the better, you have no problems with CCC here. However you are doing a lollipop ring which is regulations compliant but not standard.
Assuming the current you mention is on 110V side: volts*amps is equal on both sides of a transformer so 110*30 = 230*amps so amps =110*30/230 =14.3A
Voltage dropped over a resistance is V=IR, the (theoretical) resistance of the cables is known (for 10mm and 10m = 0.018 ohm for 8mm(2*4mm) and 10m =0.023 ohm total 0.041 ohm) current =30A do V=30*0.041=1.23V, these values are normally lower than doing volt drop = (mV/A/m*I*L)/1000.
As Tony says 1.23V dropped on 110V side is 1.11% (if the current was 30A on the 230V side then the Vd would be 0.53%)
redface
Listen to Tony more than me, at least he knows what he is talking about.
transformers
redface,
Knobhead,