Hi folks i have just tested a saw mill and the earths have be transposed from the main building to the sheds with no rods in place.

Any idea what the reg is which says a rod has to be fitted?
 
Without any info we can't reply ....

What is the nature of the supply system?
What size earthing?

come on scotch you know better than to just ask a blank question!
 
Depends what size the 4 core SWA cables are, and if there is any extraneous earthed metalwork within these sheds...

Extending a TNC-S/PME equipotential zone is not in itself against any regulations...
 
What is the size of the incoming supply this will determine the requirements for equip' bonding thus the options you have if your 16mm isn't sufficient.
 
Explain your comment please.... We are not allowed to create or extend a PME set-up thus im confused by your comment?

DNO's will often allow a single supply to be distributed between large metal units, its where there is more than one supply, diverted neutral currents from several supply's may become problematic.

Probably not relevant to the op, just an of the cuff remark.

Chris
 

Reply to Transpositon of eaths. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
912

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
662
loz2754
L
  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top