I've used 150, 185 and 240mm trip flex on large installs before contained in metal trunking.
Is there any reason I can't use 35mm for a 100amp 3phase install contained in plastic trunking? Bend radius and access is going to be tricky and a pain with solid core.
 
Any fine stranded conductor must be terminated with either a ferrule or crimp or similar.

The only exception is when using it with specially designed spring loaded terminals.
 
Any fine stranded conductor must be terminated with either a ferrule or crimp or similar.

The only exception is when using it with specially designed spring loaded terminals.
I would have thought that fine stranded would be OK without a ferrule in any terminal where the screw doesn't bear directly on the conductor. Cage clamp, for example.
 
I would have thought that fine stranded would be OK without a ferrule in any terminal where the screw doesn't bear directly on the conductor. Cage clamp, for example.

Well there is an actual reg covering this not that I can remember it off the top of my head, but no, even cage terminals need a ferrule or similar. Over time the fine conductors will still settle inside the cage and it will prove to be a loose connection over time.

With spring loaded terminals, the pressure is constant even when the copper settles. So it avoids the issue.
 
Well there is an actual reg covering this not that I can remember it off the top of my head, but no, even cage terminals need a ferrule or similar. Over time the fine conductors will still settle inside the cage and it will prove to be a loose connection over time.

With spring loaded terminals, the pressure is constant even when the copper settles. So it avoids the issue.

I would contend that, as long as the terminal is a suitable size for the conductor, ie not a stick in a bucket, that a cage clamp terminal is OK for fine stranded. In fact, I have had problems getting a reliable connection with 6mm² bootlace ferrules in cage clamp terminals due to the problem of getting sufficient pressure on the terminals to stop the rigid ferrules moving in the clamp. Obviously, a ferrule in a direct screw terminal would be a different matter.

The reg is 526.9.1: "In order to avoid inappropriate separation or spreading of individual wires of multiwire, fine wire or very fine wire conductors, suitable terminals shall be used or the conductor ends shall be suitably treated."
 

Reply to Tri-flex instead of solid tails in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top