H
Hobsoni
Hi there, Have been carrying out testing on some 3 phase sub-DB's that have outgoing supplies to 3-phase DB's for accommodation blocks. My problem is to do with readings I'm getting on a ground fault relay which has been set to 300mA. Basically, the incoming cable to the Sub DB ( 4-core 25mm SWA) enters the panel and passes through a sensor (toroid) and then terminates into an MCCB. As per the installation requirements for this Toroid device, 3-phases and neutral pass through the centre and the CPC does NOT pass through the device. From this Toroid are some control cables to a Relay which can be set (mA) and time delayed (0.06, 0.1 ms etc) and also from the relay are outgoing cables to the incoming MCCB (I presume Shunt control?) and also from the relay to the outgoing L1 terminal of the incoming MCCB. In a nut shell, whilst performing trip times on the ground fault relay I cannot get trip times less than >310.0ms whether I test at 300mA or 500mA. The device does not trip at half the rated current which is good. I am absolutely stumped, because there are 5 of these devices and each and everyone is the same!? All other readings obtained have been absolutely fine, ingoing loop to DB etc etc. I am absolutely perplexed, can someone please shed some light on what it could be please. Many thanks