Hi People.
We have a tripping MCB on a job from 8 years ago. This is the 3rd SMA inverter job to be doing this. One was because of a faulty cable in the inverter. Second, we never found out what it was, but did all tests and inspections on all connections and in the end changed the MCB to 20A from 16A (2.5mm cable) and haven't heard from her since (which I take as good news) . Now we have a third.
If any of you have tried to use the SMA helpline you'll know they aren't very helpful.
We have done a full spectrum of tests, r1+r2 (and N), IR, Zs, Ze. and a visual inspection on every connection. All is fine, but still the MCB trips after being on for a while (a few hours or a day). We have replaced the MCB but it still continues.
It's a SMA SB 2500 (so has a transformer).
Any ideas, or anyone come across this before?
Cheers
We have a tripping MCB on a job from 8 years ago. This is the 3rd SMA inverter job to be doing this. One was because of a faulty cable in the inverter. Second, we never found out what it was, but did all tests and inspections on all connections and in the end changed the MCB to 20A from 16A (2.5mm cable) and haven't heard from her since (which I take as good news) . Now we have a third.
If any of you have tried to use the SMA helpline you'll know they aren't very helpful.
We have done a full spectrum of tests, r1+r2 (and N), IR, Zs, Ze. and a visual inspection on every connection. All is fine, but still the MCB trips after being on for a while (a few hours or a day). We have replaced the MCB but it still continues.
It's a SMA SB 2500 (so has a transformer).
Any ideas, or anyone come across this before?