wondered if anyone can help me out with this;

I've recently changed a very old consumer unit over to a new split load 17th edition version.
The premises is a small bungalow with just one lighting circuit.
When i re-energised the board this particular lighting circuit kept tripping out the rcd. It has to go on the rcd side because it incorporates the bathroom.
With the old fuse board it wasnt detecting any fault so I guess this must be a N/E fault somewhere. I went round to check for any blown lightbulbs but no joy.
Anyone identify a possible fault with this?

Also the main gas and water are bonded and I am wondering do I have to supplementary bond anywhere? I have checked in OSG and am still not sure. There are no existing bonding cables other than the main gas and water bond.

Many Thanks!
 
only solution is IR testing the circuit. break circuit at each fitting and trace fault. supplementary bonding is required on any exraneous metal parts that may introduce an earth potential. i.m a bit concerned with your new CU. you say it's 17th, but then you say " on the RCD side". a 17th board has 2 RCDs and under the 17th Edition, virtually all circuits must be RCD protected.
 
Last edited:
Well apart from a N-E fault it could be

Neutral connected onto the wrong bar
Low insualtion resistance on cables if they are old
Reverserved polarity somewhere ie N/E L/N
Faulty RCD
Though unlikely in a bungalow with just a single lighting circuit but don't rule out a borroewd neutral somewhere
Outside lights with dampness

As for the supplementary bonding regulation 701.415.2 covers that.
 
you are talking about a high integrity board, we are talking about
It has to go on the rcd side because it incorporates the bathroom.
Also the main gas and water are bonded and I am wondering do I have to supplementary bond anywhere?

providing all main bonds are in place, rcd protects all circuits in location and disco times are met then no supp bonding required.

have you tried swapping lights to other rcd or fitting rcbo on unprotected side?
 
Last edited by a moderator:
part pee is a little known building regulation that says you can't do this type of work unless you shell out oodles of cash to a scam provider every year and prove your competence to them. there is NICYUK, Elecsa, Napit, BSI. but if you are a registered plumber, you can do what you want, who cares.
 
because if it has to go on the rcd side, then fitting an rcbo will still give the required protection but remove it from the rcd side. If there is a fault on the lighting circuit and then the other rcd (if there is one?) or the rcbo will trip anyway but the fault wont take out the rest of the circuits untill resolved.
 

Reply to tripping RCD and bonding question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar threads

Ok I’ll try this when I’m down
Replies
4
Views
341
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
570
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top