I have literally just had a phone call from the customer I saw today after doing an EICR and he says one of the RCD's is now tripping every half hour or so.

There were 3 CU's in total so I am back tomorrow to finish off. I didn't have time to test each circuit on the third CU but I did find poor global IR readings (L/N - E) of 0.008MΩ.

Trip time for the RCD was 43mS.

Its a TT with a Ra of 43.4.

He is currently having the property replastered (ongoing) this could be the reason for the poor IR, but I cant understand why it is tripping now when it wasn't before. He seems like an honest chap so I believe him.

I always spend the last part of the day making sure connections are tight so I'm pretty sure thats not the problem.

I'll break the circuits down tomorrow and find the culprit, but it was more the fact thats its tripping now and (most likely) wasn't before that I can understand and could do with a few opinions?
 
One of them could be anything things I would think.

Few ideas could be a weak mech that now wont hold after you tested it?
If the house is currently being plastered wet plaster shorting out something?

Sure some of the others will give you some other/better ideas :p
 
Sounds like a neutral to earth , if it's holding when you flick the rcd back on then I imagine it's tripping when a load is connected and the heat builds up . I've had it before when all is reading clear and holding and then as soon as anything is connected it trips nightmare
 
afraid that without being there it's just guesswork. sod's law says it's tripping since you were there. only thing is for you to go back and trace the fault. let us know what you find.
 
I'd retest the IR on the "suspected" circuit, repeating the test quickly to see if the IR increases - if it does it would suggest damp. All you can do then is wait for it to dry.

Plastering does mean that A LOT of moisture is "tracking" across the surfaces so good luck finding it!
 
I feel a bit of a --- adding this next bit and wasn't going to but you need all the information!

I was tired and tested at 500V by accident and got about 0.04MΩ, then tested at 250V and it went lower (0.008MΩ) which didn't make sense, unless it's the putting 500V through that did it?

I'm sure it was ok after that for an hour or so though (before leaving)! The very last thing I did was test the RCD, can actually testing the RCD produce problems?
 
I feel a bit of a --- adding this next bit and wasn't going to but you need all the information!

I was tired and tested at 500V by accident and got about 0.04MΩ, then tested at 250V and it went lower (0.008MΩ) which didn't make sense, unless it's the putting 500V through that did it?

I'm sure it was ok after that for an hour or so though (before leaving)! The very last thing I did was test the RCD, can actually testing the RCD produce problems?

I would doubt it unless you shoved 500V up it.

I'd ramp test the RCD again.

Sometimes, when its late you go round and round in circles, so walking away and going back tomorrow, with a clear mind, is probably the best plan
 
I'd retest the IR on the "suspected" circuit, repeating the test quickly to see if the IR increases - if it does it would suggest damp. All you can do then is wait for it to dry.

Plastering does mean that A LOT of moisture is "tracking" across the surfaces so good luck finding it!

Thanks Murdoch..

Could you explain this a little please?
 
Testing at 500v isnot a problem as long as all electronic equipment is shorted or removed. Otherwise it will just damage the item that is not. (Blown a neon or 2 on spurs doing this :p)

Not sure about RCD's but like I said before it could be a weak mech, We worked on a circuit once and when we put the MCB back on it just wouldnt hold despite everything being tested ok. Changed it for a new one and it held fine.
 
I would doubt it unless you shoved 500V up it.

I'd ramp test the RCD again.

Sometimes, when its late you go round and round in circles, so walking away and going back tomorrow, with a clear mind, is probably the best plan

Very true Murdoch! I realise 9 hours probably isn't very long for some sparks.. but I was a bit on the tired side.. even after a quick fix of chocolate and coffee!

Testing at 500v isnot a problem as long as all electronic equipment is shorted or removed. Otherwise it will just damage the item that is not. (Blown a neon or 2 on spurs doing this :p)

Not sure about RCD's but like I said before it could be a weak mech, We worked on a circuit once and when we put the MCB back on it just wouldnt hold despite everything being tested ok. Changed it for a new one and it held fine.

Thanks Tiny.. If all else fails I'll change it, but I'll get to the bottom of the low IR readings first.
 
Agree with Murdoch I have done the same thing many times, think of it as an expensive hair dryer
 

Reply to Tripping RCD since testing? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Ok I’ll try this when I’m down
Replies
4
Views
398
L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
670

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top