tripping rcd | on ElectriciansForums

Discuss tripping rcd in the UK Electrical Forum area at ElectriciansForums.net

Joined
Nov 13, 2008
Messages
53
Reaction score
1
Hi All. I was called out today to a tripped RCD in a domestic split board that not would reset unless the main switch was off. All mcbs off, all phase conductors removed in case of stuck mcb but still no rcd reset unless main swith was off. Any ideas, householder was not prepared for more extensive exploration at Sunday rates. Going back to-morrow.
 
Last edited:
Hi All. I was called out today to a tripped RCD in a domestic split board that would reset unless main switch was off. All mcbs off, all phase conductors removed in case of stuck mcb but still no rcd reset. Any ideas, householder was not prepared for more extensive exploration at Sunday rates. Going back to-morrow.


No power over night??
 
It can only be a neutral to earth fault but how can there be a fault at the rcd if no circuits are energised?

Your MCBs will generally be single pole, so all your neutrals (and CPCs) will still be connected. It doesn't take much voltage to push 30mA through a N to E or a N to N short.

What's the earthing system?
 
As already stated it will be a N-E fault.......I'm somewhat flabberghasted that as an arms member this isnt something you have come across before.
I'm probably more flabbergasted than you! I inspected the installation today expecting to find the N-E fault we would all expect. All circuits IR tested, no faults. 8 Meg ohms L-E on one ring final circuit but that was all.
The rcd behaved and tested as one would expect when everything was back together. My original question still remains but I will re-phrase it.
Why does an rcd trip when there is no current passing through it?
 
It seems the House Holder has removed a faulty bit of equipment like an Iron, or something, or you have corrected the fault when putting the Neutrals back in the correct RCD places maybe, or did i miss the point LMAO its l8 for my old eyes.
 

Reply to tripping rcd in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
834

Similar threads

My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
341
  • Question
A kettle boiling fish - thats your fault right there... or is it a red herring? :)
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top