got a keen apprentice who never stops asking questions which is good but not on a monday morning when you dont feel to clever anyway he was asking me how low would your ir reading have to be to trip breaker i explained that min value was 1M ohm but he wanted to now how low the reading would be to trip it help lol
 
R = V/I

R= 230/0.03 ( for a 30mA RCD

R= 7666.66666666666666666666666 ohms

or if you got a real voltage of 240V. 240/0.03 = 8000 ohms.
 
ohms law use it to find current flow depends on mcb size and time curve too as to how long it takes to trip, and also the existing load on the cable needs accounting for-, 1M ohm is very high resistance still but is an indication that the insulation value has been compromised and needs investigating but its not low enough to be a direct issue if the value is held.
 
well it would be the tripping curre, found onm the time/current graphs, or for instataneous values can be calculated. This would then be inserted into the formula R=V/I, so to trip a 10A C type in 0.1 to 5 secs, you need 100A. 230/100= 2.3 ohms maximum, or 0.0000023 Mohms.This is also your max Zs (not corrected for temp).

for 30mA RCD's it is 230/30x10-3 = 7.666ohms or 0.0077 Mohms.

For interest, this isnt the max Zs for a 30mA RCD, becuase you use the touch voltage threshold of 50V, which gives 1667ohms.
 
From App. 3 fig 3A4 you can guesstimate at 1.45 times the breaker rating. So a 10A MCB with a 15A load will take anywhere between 16 -30 mins. to disconnect (most likely shorter due to the accumulation of ambient temperature and the heating effect.)
Or you could say a load of 3.5kW (34 fluorescent fittings) which would provide a resistance of 15 Ohms which approximates to 15A.

I did an experiment with 24 fluorescent fittings connected to a B6A before upgrading the breaker to B10A and it disconnected in about 9 minutes
 

Reply to tripping value in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
940

Similar threads

  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K
H
  • Article
Worcester greenstar combi problem Hi this is my first post so please be gentle. I have a Worcester greenstar 28i junior combi fitted in my house...
Replies
0
Views
247
Happyharry
H

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top