R

Rammie

Hi all

Main RCD keeps tripping out on main CU. Think I have eventually traced it to water ingress into an external junction box but why does it not trip out RCD on the small garage CU? Or even the breaker for the external supply on the main CU?

Thank you

Steepest learning curve of my life......
 
Is the jb between main cu and garage cu if so it will only trip the upstream rcd. The breaker in main cu isn't tripping because it's not overload. It's an earth fault which the rcd will see not the CPD. Hth
 
as this is a fault to earth, and there are 2 rcd's in the cct the fault path is going back to the star point of the transformer via the cpc or neutral, and returning back through the ccts phase and tripping the first rcd it comes across which is the one in the main cu.
that seems the only logical answer to me.

look up diagram earth fault path.
As m4tty said, it is not an overlaod fault.
 
Last edited by a moderator:
The junction box is between a supply for a pond pump and small cu located in garage, which is why I couldn't understand why it was not tripping this RCD as opposed to main one in house. Have since established customer put jb in to connect the supply cable which had been cut in half?!

Thanks for the help its appreciated.
 
there should not really be two rcds of the same type on effectively the same circuit as there is no discrimination. If there is i don't think you can predict which will be the most sensitive. If the distribution to the garage CU is in SWA , surface mounted or otherwise mechanically protected it does not have to be on an rcd protected way at the main CU and so it can be moved to prevent the nuisance tripping of the main CU.
 

Reply to Tripping.... in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
178
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Evening all, Just after a sense-check before I commit & send the quote. I’ve been asked to run in an SWA to feed a small CU that’ll sit inside...
Replies
0
Views
160
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top