I have an 8.5kw Triton Excite Plus shower, could there be a reason that it has been installed with a 50amp isolator switch, & not 40amp which Google suggests would be the compatible for a 8.5kw shower ?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Triton shower isolator switch in the DIY Electrical Advice area at ElectriciansForums.net
Thanks so much for explaining !8.5kw will will draw approximately 37A therefore your isolator needs to be the equivalent or preferably above hence 40A, a 50A isolator is actually better.