Hi anyone had a fault like this before on one of these showers as i never have and hoping i havnt missed anything.
Called to a shower tripping rcd, so assumed probably cable or isolator. Disconnected isolator, cable from cu and from shower and ir test on all cables, and continuity, all good. Replaced isolator and put back on, 3 seconds then tripped again. Disconnected shower and put cables in block then switched rcd back on and it stayed on fine so my only logical thought is that its the shower itself. Visualy inspected shower and no signs of damage. Didnt rcd test as Presuming its not nuisance tripping as rcd also protects all sockets to the house and only trips when shower on. Any thoughts please. Cheers.
Called to a shower tripping rcd, so assumed probably cable or isolator. Disconnected isolator, cable from cu and from shower and ir test on all cables, and continuity, all good. Replaced isolator and put back on, 3 seconds then tripped again. Disconnected shower and put cables in block then switched rcd back on and it stayed on fine so my only logical thought is that its the shower itself. Visualy inspected shower and no signs of damage. Didnt rcd test as Presuming its not nuisance tripping as rcd also protects all sockets to the house and only trips when shower on. Any thoughts please. Cheers.