ive downloaded some revision questions for my 2394/95 course i have booked for august and ive come across a question im a little unsure about......even when i have used the regs and GN3 to help. a little help would be greatly appreciated as there is no answer sheet for the questions. Heres the question:
consider the following circuit: A TNS system in a domestic property has a earth fault loop impedance measured at the origin of 0.46ohm. A 4mm2 twin and earth cable with a 1.5mm2 cpc feeds a cooker which is operated by a control unit which has an integral socket outlet. the cooker cable is 35mtrs long and is fed through a 30amp BS3036 fuse in a consumer unit at the origin.
1) state the max disconnection time for the circuit? ( i put 0.4 seconds)
2)state the maximum permissible earth loop impedance if the rule of thumb method is used?
( i used Zs < 0.8 x U/Ia , which gave 230/210 x 0.8 = 0.876ohm)
3)Using the more accurate method state the value of actual earth loop impedance?
(i Used 1/F(Zs +Ze(F-1)) , which gave me 1/1.2x(2.64+0.46(1.2-1) = 2.407ohm)
4) State the approximate disconnection time of this circuit should a fault of negligible impedance occur between phase and earth at the extremity of the circuit when the conductors are at their operating temperature?
(i put "wont trip")
5) state if the disconnection time is acceptable?
(i put "no")
6)what simple change could be made if the circuit does not comply?
(i put "decrease the size of the fuse")
If some is kind enough and has the time, could they check through this for me and if ive gone wrong let me know where.
thank you in advance
ive downloaded some revision questions for my 2394/95 course i have booked for august and ive come across a question im a little unsure about......even when i have used the regs and GN3 to help. a little help would be greatly appreciated as there is no answer sheet for the questions. Heres the question:
consider the following circuit: A TNS system in a domestic property has a earth fault loop impedance measured at the origin of 0.46ohm. A 4mm2 twin and earth cable with a 1.5mm2 cpc feeds a cooker which is operated by a control unit which has an integral socket outlet. the cooker cable is 35mtrs long and is fed through a 30amp BS3036 fuse in a consumer unit at the origin.
1) state the max disconnection time for the circuit? ( i put 0.4 seconds)
2)state the maximum permissible earth loop impedance if the rule of thumb method is used?
( i used Zs < 0.8 x U/Ia , which gave 230/210 x 0.8 = 0.876ohm)
3)Using the more accurate method state the value of actual earth loop impedance?
(i Used 1/F(Zs +Ze(F-1)) , which gave me 1/1.2x(2.64+0.46(1.2-1) = 2.407ohm)
4) State the approximate disconnection time of this circuit should a fault of negligible impedance occur between phase and earth at the extremity of the circuit when the conductors are at their operating temperature?
(i put "wont trip")
5) state if the disconnection time is acceptable?
(i put "no")
6)what simple change could be made if the circuit does not comply?
(i put "decrease the size of the fuse")
If some is kind enough and has the time, could they check through this for me and if ive gone wrong let me know where.
thank you in advance