Trying to get a domestic electrical safety certificate... | on ElectriciansForums

Discuss Trying to get a domestic electrical safety certificate... in the Domestic Electrician Forum area at ElectriciansForums.net

A

Armourer

I am trying to get a domestic electrical safety certificate so I can rent out my house in Southampton but my electrician has come up with £300 of remedial work before he will pass it. He claims the pendant light in the bathroom breaks IP rules and the law and that I can be prosecuted for it. Now I know it’s a very good idea to have it changed for IPx4 rating but it’s over 2m from the bath/shower and so only just inside zone 3, well out of reach (high ceiling), cord operated and never had any condensation on the lead. Installed before 1999, not regulated and certainly not a criminal offence! In the kitchen he reckons that a 32 A 1.5m radial to one double socket for tumble dryer and washing machine (max load 5kW) needs to be uprated. Yet by my calculations the 2.5 mm2 cable could happily run 7kW over 10m. Some others I won’t bore you with, so my question is what action could/should I take with an electrician who is either incompetent or (more likely) just trying to pad a bill and expects to be paid his inspection fee and how do I go about finding a decent electrician if I can't trust an NICEIC contractor.
 
Well TBH he is correct by saying that the 1.5mm cable protected by the 32A OPD needs upgraded. The pendant light issue could be sorted for next to nothing by changing the standard lampholder to a TRS lampholder.

EDIT

Sorry 1.5M of 2.5mm cable. Still a 2.5mm cable can not be protected by a 32A OPD but the solution here would be to decrease the OPD.
 
I am trying to get a domestic electrical safety certificate so I can rent out my house in Southampton but my electrician has come up with £300 of remedial work before he will pass it. He claims the pendant light in the bathroom breaks IP rules and the law and that I can be prosecuted for it. Now I know it’s a very good idea to have it changed for IPx4 rating but it’s over 2m from the bath/shower and so only just inside zone 3, well out of reach (high ceiling), cord operated and never had any condensation on the lead. Installed before 1999, not regulated and certainly not a criminal offence! In the kitchen he reckons that a 32 A 1.5m radial to one double socket for tumble dryer and washing machine (max load 5kW) needs to be uprated. Yet by my calculations the 2.5 mm2 cable could happily run 7kW over 10m. Some others I won’t bore you with, so my question is what action could/should I take with an electrician who is either incompetent or (more likely) just trying to pad a bill and expects to be paid his inspection fee and how do I go about finding a decent electrician if I can't trust an NICEIC contractor.
Is the ÂŁ300 including the original inspection fee?
 
2.5mm radial just needs a 20a OCPD.....Pendant based on your description should not attract a code.
First port of call if you have employed an NICEIC contractor and you are not happy is the NICEIC complaints proceedure.
 
The pendant issue if outside zone 2 and not reachable by persons readily standing in a bath or shower would warrant only a C3 at worst. Only attribute this due to conditions of dampness and rising steam. Certainly not a danger just a non compliance depending on how you view the fitting and the conditions it is installed in,
The 1.5mm2 cable is a C2. ÂŁ300 does appear to be a bit steep. How big is the dwelling?
 
The Light Fitting what was his grade for it C3 or ?

Im thinking the Sparky could be looking at the fact that a radial 2.5mm has exceeded the 2kw rating for a radial but im looking at long periods of time on the radial( Reg 433.1), providing reasonable sharing of the load around the ring circuit as well, thats why a Washing machine and a Dryer could be best served on maybe two seperate fused Spurs on the ring etc.

The Periodic report is the report You should have been using not a Insulation Report anyway.
 
No, the inspection fee is separate. ÂŁ240+VAT is for replacing a socket, couple of marker sleeves, derating an MCB by swapping for an unused one, replacing main earthing conductor wire, replacing & re-siting bathroom light and uprating 1.5m radial. Bout an hour if he stops for tea. Small 3 bed semi btw.

Radial is direct from consumer unit in kitchen, 32A MCB, so yes if there's a reg I'm not aware of regarding 32A radials and 2.5mm cable over such a short distance I'll just derate to 25A. Thanks Sintra.

No ratings at all have been provided for any faults so unable to say whether they are C2 or C3, sorry.
 
Last edited by a moderator:
No, the inspection fee is a separate ÂŁ115. ÂŁ300 is for replacing a socket, couple of marker sleeves, derating an MCB by swapping for an unused one, replacing main earthing conductor wire, replacing/resiting bathroom light and uprating 1.5m radial. Bout an hour if he stops for tea.

Well over an hour but certainly not ÂŁ300 worth, I would agree with that.

Have you paid him for the inspection?
 

Reply to Trying to get a domestic electrical safety certificate... in the Domestic Electrician Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
740

Similar threads

Thanks mate for the advice, this is just what I was looking for. I think I’ll have to put some thought into the domestic route due to the NVQ and...
Replies
2
Views
358
Cheers mate đź‘Ś
    • Like
Replies
2
Views
614

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top