Nobody is saying it's not a good idea or that it's not good practice, but it's not mandatory.
OK
My take on the precautions to implement when omitting an up front RCD on a TT system. Tails Clamp seems an absolute necessity in my view.
There wasn't a switch to strictly use a metal consumer unit, but one made of non-combustible material.
You could still use a plastic Cu, in fact, plastic ones are preferred in some locations.
Just quoting what the article said.
Just because you may have double insulated Swa isn't a good enough reason to omit the upfront Rcd that's being used for fault protection.
The suggestion of double insulated SWA was to avoid the joint that would be required to double insulated tails not as a reason to avoid RCD protection. Omission of up front RCD protection can be considered if the tails are fully protected (from contact to the earthing system) up to the point of termination. My point was that I wouldn't consider a joint as meeting that requirement.
PS Electrics said:
Should we NOT be earthing the armoring in this case if doing away with the RCD protection? On a TT we won't meet the disconnection time requirement for an earth fault and so if the SWA is earthed and such a fault occurred we have just made the whole installations earthing live!
The Swa armour Must be earthed, otherwise a penetration of the armour could cause fatal electrocution.
My point was if we have an SWA with no RCD protection then connecting the SWA armour to the Installations earthing arrangement would be a bad idea.
As I said installing an up front time delay RCD avoids all the above issues.