Hi Guys, I was called out to a house in the countryside to do a shower replacement. The homeowner had already got the plumber to install the new shower, (an 8.5 kw to replace a broken 9.5 kw model) and wanted me to connect the shower an issue a Minor Works Cert.

I do all my tests on the wiring (6mm T+E fed from a 32amp type B MCB protected by a 30ma RCD) and everything seemed normal. R1+R2 is 0.13 ohms, Insulation Resistance is 500M.

I turn power on and check the EFLI and it turns out to be 0.54 ohms?? This is strange i think on a TT, so i look at the service head, no earth connection. 16mm earth from the Consumer Unit to a Henley block in the meter cabinet, and a 16mm earth going into a duct and underground. No sign of any earth electrode??

I do a Ze and it is 0.47 ohms. So i ask the homeowner if he knows the position of any earth rods and he tells me "the ground was too rocky, so my father-in-law connected the earth to the earth at the pole"

I've not come accross this before and dont know how to proceed so any opinions or advice would be appreciated.
 
Call the DNO and get them out to sort it out.
There may well be a very good reason they did not make their earth connection available to the consumer so making a DIY connection to their transformer's earth is not good!
 
DNO's are now supplying overhead PME systems to rural areas providing a stable earth for customers. These are easy to spot following the line of the overhead poles and at about every 3rd pole you will see an earth coming down the pole into the ground.

The earth though is the property of the Network provider and can only be issued with there permission. After all ithey have to guarantee it's stability to the ESQCR. So your FIL "nicking" the earth is not a goer.

You will have to contact the DNO before they find out to be honest.
 
I have only encountered pnb once, in similar circumstances as described in the opening post. I couldn't see where the earth was taken to. For the sake of a quick call to the dno a lot of speculation could be avoided
 
You need to contact the DNO, the TX will be either hot or cold with regards to earthing, you could see some dangerous voltages on your installation if a fault on the TX occurs.

Cheers
 

Reply to TT Earthing using DNO Rod at Transformer?? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
834

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
947

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top