E

easysushi

Alwite lads,

Replacing a consumer unit today in ex council house. Got Earth fault loop of 537 Ohms, after playing around and finding the electrode which was a steel pipe I replaced the Eath cable from 10mm to 16mm and drove a 1.2 mtr copper rod in got a value of 410 Ohms. Then drove another in the front garden lawn dropped to 360, stuck another in got 300, stuck another in got 200, stuck another in got 130Ohm.
So i have got 5 rods in the ground at the moment. Obviously the customer is not to keen to have so many inspection pits in there frount garden .

Any Ideas would be very much appriciated, or am I missing something :rolleyes:
incoming supply is over head


Cheers


Ty
 
Last edited by a moderator:
Depending on the soil conditions you may be better off with a different type of electrode altogether, eg. a plate or tape electrode, or a much longer driven rod electrode.
 
Assuming you are using an insulated dual 30mA RCD consumer unit, there is no need for a 100mA RCD.
The 30mA RCDs would give a max. permissable Zs of 1667 Ohms in theory, but you must achieve an electrode Ra of <200 Ohms to ensure stability of the earthing arrangement.

Personally I would use rod electrodes with threaded ends and screw-on couplers, keep driving them in and joining new lengths on until a satisfactory reading is achieved, then dig a hole around the top and install a pit and lid.
 
Assuming you are using an insulated dual 30mA RCD consumer unit, there is no need for a 100mA RCD.
The 30mA RCDs would give a max. permissable Zs of 1667 Ohms in theory, but you must achieve an electrode Ra of <200 Ohms to ensure stability of the earthing arrangement.

Personally I would use rod electrodes with threaded ends and screw-on couplers, keep driving them in and joining new lengths on until a satisfactory reading is achieved, then dig a hole around the top and install a pit and lid.

Mate I know it has to be <200 Ohms but what would you consider to be and accetpable reading with a single rod, ok maybe 4 x 4ft rods linked together.


Cheers


Ty
 
Depends entirely on the soil conditions, 90 percent of the time I get below 200 Ohms with a single 4 foot rod. In your case sounds like you have soil with high resistivity so it's gonna be hard work whatever you do, eg. very long electrode, multiple electrodes, plate or tape etc.
 
just did a caravan and the readings were 36 ohms with a single 38 mm rod , have a look round and find what looks like a damp spot , one of the best places ive found is near sink outlets or down pip[e gullys because that area tends to always be damp
 
Depends entirely on the soil conditions, 90 percent of the time I get below 200 Ohms with a single 4 foot rod. In your case sounds like you have soil with high resistivity so it's gonna be hard work whatever you do, eg. very long electrode, multiple electrodes, plate or tape etc.

The soil around the area is very sandy. I gues that would give cause to high resistivity do you think


Cheers


Ty
 
yes im affraid it would , i did a temp caravan supply in a sandy area by a beach couldnt get a decent reading in the end i ran a 25mm earth 30 meters and sunk it in a stream got the reading down to 76 ohms , try a rod as close to the house as you can yu may get better readings also try lower ground so any water runs in it , the wetter / damper the area the better , could be an idea to use a tape or plates to
 
Well 4 rods later and sweating like a ******, driving the rods down got 69 Ohms. A lot better then the 500 I had to start with

Thanks for all your advice guys


Cheers


Ty
 
Last edited by a moderator:

Reply to TT Help in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
181
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top