P

pjb1

Went to see a mate today who's a chippy has a smallholding on a farm. While standing there gassing about dirt bikes the Blokes who have the unit next to him. Seem to be having problems my mate being nosey asked what was up. Big mistake, The chap said their rccb kept tripping, Guess what was coming my mate’s points at me and says he's a sparky. Don't you just want to hit them when they open their mouths?
Anyway not being one to not offer to help if I can. Went and had a look. In the unit was a 40A 30m A 3phase RCCb which feed a 3 phase switched fused isolator. Feeding the 3 phase Rccb was a 4-core swa, the earthing conductor was a 10mm single terminated on the side of the switch fuse isolator. clipped and passed through the external wall to the earthing electrode sited in a pit.
The cause of there problem was, off the top of the 3 phase switch fuse they had a single phase supply feeding a cu which feed the lights and sockets. And when they plugged anything in, it was taking out the 3 phase Rccb.So they hade disconnect the consumer unit, And using those tails in connector block (Using this for a test purpose) used it as a direct feed for a belt sander, But switching on the sander still knocked out the 3 phase Rccb. Nothing at fault with the belt sander tested that else where.
I removed the tails to the top side of the Rccb giving it now a direct feed from the supply. Turned it on even though the belt sander was working, it still took out the Rccb? Checking all termination for loose connections looking for something that maybe causing a high resistance, all terminations checked out fine.
Anybody shed any light on this one?
 

Reply to TT help in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
801
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
833

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
703
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
947

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top