TT installation help | on ElectriciansForums

Discuss TT installation help in the UK Electrical Forum area at ElectriciansForums.net

W

Welshsparky

Hi all

Job on a farm, which is TT, The supply conductors go into a 100 amp 4 pole RCD Mainswitch ( In a plastic Enclosure) Then off to an MCCb Board which then feeds Several sub mains around the farm that all Have 30 Milliamp RCD Mainswitch

Problem the customer has is when their is a fault at one of the sub mains IE - House or office, This trips the Main RCD for the installation before tripping the 30 Ma's Rcd at the submains, Would installing a a 100ma time S type solve this problem? If not Can anybody advise me what would?

Many Thanks
 
I assume that there is a BS 4293 30mA RCCB in the main board?
If so there is not much chance of earth fault discrimination between two RCDs in series.

IMO, I would try either a 100mA or 300mA 'S' at the main board and test downstream at each of the other 30mA protected boards....
 
The Rcd were the fault occurs will trip, but the Rcd at the supply will always trip aswell. resulting in having to reset the rcd at the sub mains, Then having to go out to the barn to reset the one at the supply also
 
The Rcd were the fault occurs will trip, but the Rcd at the supply will always trip aswell. resulting in having to reset the rcd at the sub mains, Then having to go out to the barn to reset the one at the supply also

may be worth testing the rcds,is there a reason for the tripping any signs of rodent damage in the outbuildings,had the same with rat chewed cables....
ps wear gloves when looking
 
Had this problem with a garden install. 100mA RCD protecting the main installation and a 30mA covering the garden shed.

Tested out Ok at 1/2 and 1 times IAN but tripped both out on 5 times IAN.

IMO to reduce nonsense tripping then replace the main RCD with eaither 100mA or 300mA 'S'
 
Had this problem with a garden install. 100mA RCD protecting the main installation and a 30mA covering the garden shed.

Tested out Ok at 1/2 and 1 times IAN but tripped both out on 5 times IAN.

IMO to reduce nonsense tripping then replace the main RCD with eaither 100mA or 300mA 'S'

I hope not all of the house installation was relying on 100mA :)
 

Reply to TT installation help in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
947
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
957

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top