I'm a bit confused about the values taken while testing a TT installation. I need enlightening.

Sub main from house 16mm SWA into 4 way CU with 30Ma main switch/RCD.
16mm earthing conductor.

1 ring
1 radial sockets
1 light circuit

Ze = 164 ohms
PFC = 1.4 amps
Zs of ring = 184 ohms

R1+R2 ring 0.34 ohms
R1+R2 radial 0.05 ohms
R1+R2 lights 0.85 ohms

Comments appreciated.
Harry
 
The Zs would usually be less than the Ze and R1+R2 values.(especially, much reduced, if there are parallel earth paths)

Is the rod local to the sub main load end or at the supply side ? (did the testing include the R1+R2 of the SWA) It still would not make up the 20 ohm excess

If not, was this value obtained with an earth loop tester, with the" no trip" function, which is sometimes very inaccurate and therefore ignorable?

Your reading is within recomendations.but there is a question mark against those stated values

The PFC of 1.4 amps ,unless you meant 1400 Amps and forgot the K or you are measuring the prospective earth fault current only
The prospective short circuit current would give a much higher reading than the earth fault current in a TT system
 
so apart from the discrepency between the r1r2 and zs compared to the ze reading, everything is ok you think?

on the test results cert, the section which asks for the max Zs permitted by 7671, what value should i put? 1667?

thanks
 

Reply to TT installation queries in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
864

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top