We have just moved into a house built in the 90's. So, I'm a retired electrician and was confused by the 4 x TT rods all connected within a metre of each other on one side on the house. I dont have any expensive test kit any more, but when I connected an electric fence energiser to the house earth I only got 1000v instead of the 7000+v. when I ran a test earth independent of the TT system I got the full voltage. I decided to put in a new 3/8 rod and therein lies the problem. The house is surrounded by rubble and you can hammer in a rod and then literally just pull it out again by hand. Nearest proper soil is 15m from the house. Any suggestions would be gratefully received. Ta.
 
Linian make some very handy accessories here. One is a rod-tip that is basically a masonry drill:
And they do a matching SDS driver to make it easier to drive in:

If you can get 8' in (two 4' rods with coupler) generally you get better results as ground tends to retain moisture lower down. However, if it really is dry rocky stuff all the way you might want to consider a trench to somewhere that has soil for a rod with better chance of success.
Thanks for your advice. will get this bit and maybe have to hunt around for some more solid ground. When I was running my electrical business I vaguely remember you used to be able to buy something like a clay to goa around the rod - will have to have a look...........
 
Thanks for your advice. will get this bit and maybe have to hunt around for some more solid ground. When I was running my electrical business I vaguely remember you used to be able to buy something like a clay to goa around the rod - will have to have a look...........

Bentonite I think it's called.
 

Reply to TT issues with new house in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
952
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
957

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top