C

carson

Just been to carry out a pir on a flat & the supply cable comes in line & neutral only & goes directly to the meter it then comes out of the meter to henley blocks which then supply the 2 consumer units, each consumer unit has an earth conductor connected into the henley block for the neutrals. is this wrong as i think this would tt to tncs conversion carried out on the consumer side of the supply
 
It sounds like a nasty DIY PME conversion.

When you say the supply goes directly to the meter, do you mean it's unfused?
 
I'm sorry lads maybe i should have explained it a bit better, this is a second floor flat the main 3 phase supply comes in on the ground floor to an understair cupboard it is then split up & fused & the seperate cables go up the service ducts to the individual flats, this is all done as you would expect with a 3phase & neutral supply at the origin with a seperate earth conductor coming into the main cut out enclosure which is then linked to the neutral. To me this is a typical tncs supply but after the supply cable comes into the flat i have the problem detailed in the previous post.
 
Well by the sounds of things and before we even go down the BS 7671-2008 road, what you have described is very much against the ESQCR-2002 statutory document and regulation 8(4) let alone our regs..

I can't remember the old Electricity Supply regulations one but a bit I do remember is that they also banned the use of TN-C within the installation.

So if that is what you have I think it may need a little remedial work.
 
Thanks for the replies lads the wiring installation within the flat is one of the worst i've seen e.g loop in lighting using only 2 t&e using the cpc as live conductors, no main or supplementary bonding etc etc. I've just never seen a tncs supply converted to tt by the supplier then converted back to tncs by the original installer.
 

Reply to Tt or tncs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
813
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K
  • Question
No, that is part of a different earthing system, don't mix the different earthing systems unless you have given proper engineering consideration...
2
Replies
27
Views
3K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top