Went to look at a job this morning - additional socket in free standing garage.
The supply is fed from FCU in kitchen via a 2 core Hituff cable. There is a separate earth (10mm) that appears to be
TT'd at the garage, but without digging it up - i can't verify the termination. The Zs is 19.5 ohms and is protected by
a MK LN5760 DP 30mA RCD.
The customer has asked me to upgrade the cu to 17th edition and is prepared to change the supply to the garage, but it
would only be replacing the hituff with 3 core to provide suitable earthing.
As a TT supply the 19.5 ohms is acceptable, but is the supply allowed to be taken from a FCU on an existing circuit? I
would prefer it to be an independant circuit.
Thoughts please, as i don't want to charge customer if it doesn't need doing.
Thanks