D

domestic spark

When making a supply type TT what is the smallest cpc you can use from the rod to the MET thanks I'n advance. From orign to DB 25mm tails. Bs1361 type 2 main fuse. 100a
 
all depends on the Ze and PFC. as long as the cable will stand the PFC. say you had a Ze of 20ohms, PFC would be 11.5A. generally 6mm is sufficient.
 
Last edited:
You can if you wish and calculate as Tel said, go down as low as 2.5mm as per regulation 543.1.1 if it is mechanically protected, if that is what the Adiabatic equation gives you.

Think you find that most sparks will opt for either 4mm/6mm. Even if the calculations came up to under 6mm I would normally not go less than 6mm go with that on a TT, but that is just my opinion.
 
if you use 10mm i wouldn't worry unless you got a ridiculously low Ze and high PFC. e.g. Ze below 5ohms. PFC above 50A
 
6 or 10, depends on which is easier to find in the rat's nest i call my van.
 
well if you use a 30mA protection device, you can in effect have 1667 ohms, and it would still work! so you could in fact just place a nail in the wall with a 1mm cable attached to it! haha, it is fact, but not recommended.
 

Reply to TT supply type in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
791
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
612
This is the point of having a trainee badge... it allows you to ask simple questions without the critism reserved for have-a-go heroes. Things...
Replies
5
Views
444

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top