Just finishing off cert for a TT system, got a Zs of 115 ohms throughout. will I be right in thinking the max Zs column for all circuits will be 1667 or 200?
Cheers
Cheers
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss TT system and Zs results in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Just finishing off cert for a TT system, got a Zs of 115 ohms throughout. will I be right in thinking the max Zs column for all circuits will be 1667 or 200?
Cheers
For a non time delayed 100mA your maximum Zs would be 500 ohms, if all the circuits are protected by the 30mA RCDs then max Zs is 1667 ohms.
Ra x I delta n <= 50V
so 50V/0.03s = 1667 ohms
50V/ 0.1s = 500 ohms
The time delay causes problems for disconnection times as it will add about 0.15s to the time.
Nice low Ra like that! Well yeah I think so, you are pretty much as safe with a 100mA as a 30mA gone in 0.02 seconds, or 0.17s better than .4s whatever. (sorry, of course the regulations, forgot about them: 100mA deadly!)But still well worth having as a supplementary back-up for those 30mA RCD units, on a UK installed TT system with an Ra of 115 ohms wouldn't you say?? lol!!!
One of my mates was testing for the council and on tt systems they wanted him to link the neutral to the earth at the board ( so in theory it's a tn system) to get more "true" zs readings
Pass!!!!What would be the point of linking those conductors? Any reading given would be completely worthless
I did think to myself ......hang on a minute!!! But I suppose they would satisfy the maximum zs for a change!!!! Not quite sure how the nic etc. would like it tho, but it was the councils head electrician that told him!