Out of interest....if somebody was to install an earth rod on a TT and the Ra was bang on 200 ohms, then years later you tested the earth rod at an Ra of say 280 ohms with the install value unknown to you, what would your opinion be of the person that installed it.....?
I would consider the ground conditions at the time,if it was high summer and dry ground,it is unlikely to deterorate further and will probably be at it's worst,if the ground was wet there may be cause for concern. But I would not panic as some appear to on here...considering the prime and preferred earth fault protection device will provide protection up to 1667 ohms and if it has an 100ma up front device as well then up to 500 ohms would meet the requirements.....An Ra of 280 ohms on a properly designed TT system with an S type 100ma main switch and 30ma protection to all circuits would provide exactly the same protection as an Ra of 30 ohms.
Discuss if you want.