Hi all. Can anyone tell what size the earth cable should be from CCU to the earth rod. To clarify I am installing an TT system in a two bed regular house.
 
OSG states it should be 25mm sq. if unprotected. Not sure what they mean though, would that mean clipped direct. 16mm sq. if protected against corrosion. But it says you can get away with 2.5mm sq. if protected agains corrosion and mechanical damage. Why is there such huge difference. Can the 2.5 carry the fault current anyway
 
OSG states it should be 25mm sq. if unprotected. Not sure what they mean though, would that mean clipped direct. 16mm sq. if protected against corrosion. But it says you can get away with 2.5mm sq. if protected agains corrosion and mechanical damage. Why is there such huge difference. Can the 2.5 carry the fault current anyway
Unprotected means without a sheath.
Mechanically protected means with a protective cover enclosing it, such as conduit.

Those csas are for where the conductor is buried.
Once it is mechanically and corrosion protected then it can revert to above ground levels of csa.

Calculate what the earth fault current would be with a standard TT system and you will see why 2.5mm may be acceptable if it is suitably protected.
 
As the earth rod (electrode) is going to be in place a long time, probably for a good 30 years or so, it makes sense to use 10mm cable, rather than anything thinner if it doesn't have a decent means of mechanical protection.
 

Reply to TT system cable size in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
352
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
901
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
To give you some idea....with my DNO, the question "Can you see arcing, sparking or smoking?" is 3.5 minutes into the automated call answering...
Replies
8
Views
732
  • Question
If your using 35mm or 50mm use 2 core SWA and use the armour as the earth, it'll cut down on price. I know people will comment on this but the...
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top