What value ZE do you regard as suitable for a TT then and why?

Yes of course I have informed the customer of this - his energy supplier is making a visit on Monday to see if the farmhouse is suitable fro an upgrade to 100A. Sorry if I didn't make that clear boss, it'll just have to come out of my wages I guess.

How about you tell me, you are after all the electrician on the job!! Oh and the correct term is Ra, NOT Ze when referring to a TT system.

Not sure what an upgrade to 100A has to do with anything, perhaps you can explain??
 
Not just on the Continent. In the south of Ireland ETCI Rules require an earth electrode connected to the MET on a TN-C-S (aka "Neutralised") installation.

That makes a good deal of sense to me, why it isn't the same in the UK i really don't know.
I wonder why no-one from Southern Ireland here, has ever mentioned this requirement. This is the first time i've heard of this requirement in Southern Ireland....
 
Not just on the Continent. In the south of Ireland ETCI Rules require an earth electrode connected to the MET on a TN-C-S (aka "Neutralised") installation.

A while ago I asked Marvo about supplies in SA, he sent me some pictures of a service head.

Some interesting features to it, mainly the concentric being locally earth. I’ll leave it to him to post them
 
A while ago I asked Marvo about supplies in SA, he sent me some pictures of a service head.

Some interesting features to it, mainly the concentric being locally earth. I’ll leave it to him to post them

From Marvo:
“I took the photos specially for you or maybe for Eng to show you the earthing arrangement at my house which is TNCS on a 60Amp 16mm concentric cable with a local rod at the point of supply.”

[ElectriciansForums.net] TT system converted to PME - Earth rod query
 
Not just on the Continent. In the south of Ireland ETCI Rules require an earth electrode connected to the MET on a TN-C-S (aka "Neutralised") installation.


...perhaps to safeguard against nasties happening when the laws of physics changed back in the sixties and it became a great idea to just have two conductors to each house because that works.

or...was it cheaper maybe...? Hang on......
 
Some of the early Australian distribution systems were ingenious when it came to saving money. A single MV conductor feeding a transformer and use earth as the return. Just how it worked when it was exceptionally dry I don’t know but I’d be very wary of approaching a transformer pole.
 

Reply to TT system converted to PME - Earth rod query in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
395
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
986
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
795
  • Question
To give you some idea....with my DNO, the question "Can you see arcing, sparking or smoking?" is 3.5 minutes into the automated call answering...
Replies
8
Views
744

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top