Hi

Ive read a few discussions on the topic but what setup would you recommend for replacing a DB on a domestic TT system?

I've moved house and need to get the meter changed ready for the car charger, I need to upgrade the severely dated DB at the same time.

Existing is a multi9 13 way RCD main switch DB, one of those circuits is a sub main to the garage which I'm intending on adding a car charger to at some point, realistically the only option I see is a 16 way DB, I was looking at this


The intention was to use RCBO's for the circuits which I think would allow me to keep the main switch, I think my next question is on the sub main to the garage, if this is for example a 50A 30mA RCBO in the main DB would I need to install RCD protection in the sub main or should that not be a RCBO and a separate earth ROD installed for the garage, this would prevent a fault tripping a RCD upstream.

Thanks
 
Hi

Ive read a few discussions on the topic but what setup would you recommend for replacing a DB on a domestic TT system?

I've moved house and need to get the meter changed ready for the car charger, I need to upgrade the severely dated DB at the same time.

Existing is a multi9 13 way RCD main switch DB, one of those circuits is a sub main to the garage which I'm intending on adding a car charger to at some point, realistically the only option I see is a 16 way DB, I was looking at this


The intention was to use RCBO's for the circuits which I think would allow me to keep the main switch, I think my next question is on the sub main to the garage, if this is for example a 50A 30mA RCBO in the main DB would I need to install RCD protection in the sub main or should that not be a RCBO and a separate earth ROD installed for the garage, this would prevent a fault tripping a RCD upstream.

Thanks

An rcbo or rcd in the garage and a rod wont stop it tripping the upstream one. If you could get pme then you could use an mcb for the submain, and then add more rcbos in the garage
 
An rcbo or rcd in the garage and a rod wont stop it tripping the upstream one. If you could get pme then you could use an mcb for the submain, and then add more rcbos in the garage
My only thought was I shouldn’t be exporting the Earth from the house hence the 2nd rod.

There is currently a supply to the garage where they have exported the Earth, rcd main switch on this, so I could just fit a mcb in the house and RCD main switch or RCBO in the garage

Thanks
 
My only thought was I shouldn’t be exporting the Earth from the house hence the 2nd rod.

There is currently a supply to the garage where they have exported the Earth, rcd main switch on this, so I could just fit a mcb in the house and RCD main switch or RCBO in the garage

Thanks

Nothing wrong with using 1 rod for the whole installation.

If you're keeping TT, the submain will need an rcd or rcbo infront of it won't it, think about the likely zs readings you'll be getting vs what the protective devices require to operate for fault protection. A 50A type B mcb needs 80% zs of 0.69 to disconnect. You're not getting that from any rod 🫠.
 
As I understand it, the next amendment being published to BS7671 will likely include the addition of an internal RCD to all EVC devices. However as the supply circuit may well require an RCD as well due to the existing requirements for cable installations when buried this potentially leads to a nuisance trip situation, which I think is maybe what you’re getting at. In this scenario, the minor risk and inconvenience of not knowing which device may trip under fault has been deemed not a nuisance.
 
As I understand it, the next amendment being published to BS7671 will likely include the addition of an internal RCD to all EVC devices. However as the supply circuit may well require an RCD as well due to the existing requirements for cable installations when buried this potentially leads to a nuisance trip situation, which I think is maybe what you’re getting at. In this scenario, the minor risk and inconvenience of not knowing which device may trip under fault has been deemed not a nuisance.

Yes it is really, Thats kind of where I got to in my head after reading SuffolkSpark’s post (thanks for that) I need the RCD to protect the sub main cable, the EVC has a RCD built in and if a fault were to develop then I’d have a multiple of RCD’s to reset.

RCBO is still the best setup as currently a fault will trip all 13 circuits (via the RCD main switch)

From what I’ve read a non RCD main switch is ok if using RCBO but the meter tails need to be secured and glanded?
 
Yes it is really, Thats kind of where I got to in my head after reading SuffolkSpark’s post (thanks for that) I need the RCD to protect the sub main cable, the EVC has a RCD built in and if a fault were to develop then I’d have a multiple of RCD’s to reset.

RCBO is still the best setup as currently a fault will trip all 13 circuits (via the RCD main switch)

From what I’ve read a non RCD main switch is ok if using RCBO but the meter tails need to be secured and glanded?

Yes thats right, use a wiska tails gland, some consumer unit brands also then have a clamp which also holds the tails secure at the main switch. Youll probably want dp rcbo for your ev, so if your garage board will be main switch > mcbs, make sure you use a dp rcbo at least for that garage submain in your main board.

The wylex stubbies are switched neutral which may satisfy this, just check charger instructions, as some have a built in rcd now so its fine, i fitted a podpoint yesterday that didn't, and stipulated 2pole rcbo or rcd.
 
The circuit for EVSE must not share an RCD for other circuits such as dual RCD boards unless one RCD is reserved solely for the EVSE. Your situation of a sub circuit having an RCD particularly if it is for additional protection is clouded as to whether this would be deemed as shared.
 
The circuit for EVSE must not share an RCD for other circuits such as dual RCD boards unless one RCD is reserved solely for the EVSE. Your situation of a sub circuit having an RCD particularly if it is for additional protection is clouded as to whether this would be deemed as shared.
Has this always been the case? Ive seen many ev chargers on dual rcd boards? And in many installs with upfront rcd, i don't do them often, infact yesterdays was my third ever, and they've all been on their own as luck would have it rather than planned

Edit, came in in AM2, theres a little bit about it on hagers website, but then it goes on to saying you can still come off a dual rcd board if its a type A, but the charger still needs another one of its own downstream too 🫠

Another thing to keep an eye on at eicrs i guess, the amount of dog ---- ev installs i see
 
Last edited by a moderator:
Has this always been the case? Ive seen many ev chargers on dual rcd boards? And in many installs with upfront rcd, i don't do them often, infact yesterdays was my third ever, and they've all been on their own as luck would have it rather than planned

Edit, came in in AM2, theres a little bit about it on hagers website, but then it goes on to saying you can still come off a dual rcd board if its a type A, but the charger still needs another one of its own downstream too 🫠

Another thing to keep an eye on at eicrs i guess, the amount of dog ---- ev installs i see
Section 722 was introduced in the 18th Ed and yes it has always been the case see Regulation 722.531.3.101 and should merit a Code if carrying out an EICR.
 
I would say so yes or use electrical separation. The Regulation is pretty open as to how it applies regarding a sub circuit, does the RCD only apply to that sub circuit or would the downstream circuits be considered as sharing that RCD. If the sub circuit was 30ma for additional protection I would say shared as the downstream would not need further protection although this would strictly be non compliant but needs must on existing installations. If it wasn't 30ma but an RCD was used for fault protection on the sub circuit and downstream circuits were 30ma I'm not so sure this would be deemed shared.
 
The circuit for EVSE must not share an RCD for other circuits such as dual RCD boards unless one RCD is reserved solely for the EVSE. Your situation of a sub circuit having an RCD particularly if it is for additional protection is clouded as to whether this would be deemed as shared.

Didn’t know that, learn something new every day
 
One last question regarding the RCD on the meter tails, the meter tails will pass through a cavity wall to the external meter box, my heads telling me I would need RCD protection on this if less than 50mm in the wall but just looking to clarify
 
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be:

  • 50A RCBO to feed garage db
  • Garage db has no RCD protection
  • 32A MCB from garage db to charger, charger has additional Type A RCD built in
 

Reply to TT System Existing is a multi9 13 way RCD main switch DB in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
824
  • Question
Many thanks all. Very helpful to be able to bounce these things around. Was fairly happy with it all initially, but once the seed of doubt is...
Replies
8
Views
617
  • Question
It is a TNS system, the earth rod is providing an earth reference to make on epile of the supply neutral and is not part of the earth fault loop...
Replies
20
Views
4K
davesparks
D
  • Question
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
1K
  • Question
True, though the disconnect time is for typical fault currents which would usually be much higher than In for the RCD. Still, not many MFT can...
Replies
15
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks