I did see TWO NERs in the 33 - 11 kV sub at the university...
I think the opinion is that at depths beyond 1.5m are not prone to seasonal variation, Certainly in this country.
Bentonite is a gel/slurry, create a pool and drive in your rod, it will pull the bentonite down, it will help a little but not much. Time is the best, the soil will consolidate over time reducing the Ra the most.
Your description of Bentonite is completely wrong Chris, Firstly you do not just create a pool and have the earth rod take the slurry with it.... that would be a complete waste of time and of the bentonite. Who on earth taught you that method??
Well, it's a method i've used, suggested by several chartered engineers who work for two of the largest Earthing solutions company's in the UK. where drilling and back filling with Bentonite would be to costly/time consuming. As i said create a pool and drive in the rod keep pouring the mixture and this will be drawn down with the rod, this will fill most voids around the rod and lower its resistance. Jobs a good un
Secondly Bentonite is a recognised throughout the industry as a working enhancement of earthing electrodes and as such a proven system. Your description of '' it will help a little but not much'' is totally incorrect. Maybe in the installation method that you propose, but certainly not, when used correctly!! ie, ...in a bore or in a excavated trench etc!!
Used correctly Bentonite will fulfill it's function of substanually reducing the resistivity of the surrounding soil for probably the life of the installation, as it will continually absorb water/moisture and hold that moisture, it's also in it's own right, a conductive medium.
Not disagreeing if used as a back fill, though there is a limit om the radius and its effectiveness. Though certainly in many domestic situations i don't see many drilling holes LOL. The method i mention is relatively effective without to much hassle. Though i would probably use Marconite if i was trenching, it doesn't rely on water, Bentonite can dry out.
As for the other points you brought up in your post, ...Well there certainly better than most of the TT systems that you'll find in the UK, ...that's for sure!! lol!!
Depth equals stability first and reduction of Ra values secondly. Both are important factors in creating a ''Functional'' TT system....
Tell me the name of this earthing solutions company, ....i'd love to talk to these C'eng's on this utterly useless application method of bentonite...lol!! The slurry would have to be so thin and therefore weak in bentonite content to even be drawn down with the rod!! For bentonite to be an effective enhancer, there needs to be a volume of the mixture surrounding the rod for it's full length in the soil. Having bits here and bits there, that would be so thin, it'll useless and probably dry out in next to no time!!
Check with any of the manufacturers of bentonite powder or granules and see what they say is the standard installation method!! You'll find that it is exactly the same as the Maronite method. Powdered bentonite being favoured for bores and granules for excavated trenches...
E54, consider if you were being really adventurous and went for 10 meters depth with a power hammer, the void left by the couplers would be considerable. Its one way of over coming soil consolidation.
Regards Chris
The problem with that analogy is that you were not talking about 10metres in your original post you were talking 2 metres!! But even so, even driving 10 metres you are not going to end up with a bore of 50mm or more!! Not that anyone would consider driving 9 or 10 rods into the ground. Perhaps this is why you were not impressed with the results of bentonite, and why what went into the ground didn't last very long??
Bentonite is a highly absorbing medium and will continually absorb moisture from rainfall etc. It holds it's moisture for considerable periods of time, so is even good for areas of low seasonal areas of rainfall.... But only IF and WHEN it has been used correctly. I'm not saying it's the best, it's not. .....Conductive cement or Marconite would fill that title, but it is the a good runner-up in this field!!!
DEEP EARTH GROUNDING VERSUS SHAL
http://www.copperinfo.co.uk/earthing/downloads/pub-119-earthing-practice.pdf Page 95 - 96
These are a few ive managed to dig out, im sure there is others, so im not the only one LOL.
Regards Chris
Well, im not saying the method doesn't work, it does to a degree, you drive in 3 5,8 rods and you will be surprised how much gets drawn down and there's no doubt it improves the Ra. Its a case of is it necessary i suppose, the soil will consolidate over time.
you can get a decent tt system with 2 rods driven into the ground,its what we do its in the regs we dont need trenches we dont need to drill for oil just to put a rod in,i think were over complicating matters here..
Is it France where they "insist" on an earth plate for domestic TT i.e. a large copper plate buried in a pit - or did I dream that?
I don't think were talking about the easily achievable low standard of what's required in the Reg's here. But rather in the type and/or method of installing an enhanced earth rod Alarm Man.... But i'm pleased to hear that you couple your rods to get that bit of extra depth on installations. ..lol!!
You dreampt it i think, but they do want a decent TT system at domestic installations.
But It can be by plate(s)/ rods(s) or tape, etc...
You would be willing to hold a LAMP against an earthed rod then touch it with a live cable?I have their "regs" but the French is beyond me! Onto another TT myth then - is in true that in the "olden days" they would test how good an earth you had by connecting one side of a light bulb to live and the other side to the rod - the brighter the light the better the earth. I so want to try this!
You would be willing to hold a LAMP against an earthed rod then touch it with a live cable?
Do you promise to get your mates to post the video on youtube, there's a good chance you may be unable to![]()
I have their "regs" but the French is beyond me! Onto another TT myth then - is in true that in the "olden days" they would test how good an earth you had by connecting one side of a light bulb to live and the other side to the rod - the brighter the light the better the earth. I so want to try this!
Not sure what your trying to prove with this link?? If it's driving 10 metres (several rods coupled) or more of earth rod in the ground, then as this link quite rightly points out, the good likelihood of those rods snapping or bending after hitting hard obstacles... (they won't be referring to 1.2m rods either, but 3m rods) Normally and as a matter of course, you would bore rather than drive (dependant of ground conditions) past 6 to 8 metres....
Chris, i've been involved with the creation of deep ground fields and other conventional and un- conventional grounding systems of deep and shallow earthing systems for a multitude of different purposes for over 30 years now. And in just about every type of soil condition i can think of, in different climates. I know what does work, and i also know what doesn't work, because i've had a few of them too in the early years. All i'm saying to you is, that relying on a bentonite slurry to be drawn in, as your driving a rod into the ground Won't and Can't work, for the reasons i've given you!! And probably why you were not too impressed with the results yourself...
Onto another TT myth then - is in true that in the "olden days" they would test how good an earth you had by connecting one side of a light bulb to live and the other side to the rod - the brighter the light the better the earth. I so want to try this!
Well i wasn't trying to prove anything as such, you said the use of Bentonite in the way i described was completely wrong. The method is used and it works to a degree, better than peeing on it LOL. The point i was making i suppose was that unless you are going to extreme measures soil consolidation will have the biggest effect on the Ra.
First off, it depends on what you mean by ''extreme measures'' if referring to a domestic installation yes i could agree, ...but it isn't considered so, in other applications. Oh, and anything is better than peeing on it!! lol!!...
As for Ra, No, not always!! I'm afraid you could be Wrong again, because that would depend very much on the resistivity of the soil type. Consolidation of an unfavourable soil type would make little difference to your Ra value, without a chemical or other form of enhancement. Consolidation by the way can be a lengthy process, anything from 18 mths to 5 years, again depending on ground/soil and climatic conditions (rainfall etc)
Even if you use Bentonite or marconite there's not going to be a massive reduction, roughly a 10 % reduction.
I have no idea, where you have got this 10% figure from, as it will be completely different for the type of ground/soil conditions. It can be significantly more than your stated 10% from my experience
Take a soil resistivity uniform 120 ohms, 3 x 3 meter rod's, 1 rod 15mm diameter and another rod 50mm and 100mm using Bentonite.
The 15 rod comes out at 41 ohms, the 50mm rod comes out at 33 ohms and the 100mm at 29 ohms
So if we install 2 x 3 meter rods, 1 at 15mm and the other 100mm we have:
15mm = 24.6 ohms
100mm = 17.1 ohms
If only designing an earthing system was as easy as this!!! ...lol!! Firstly, i've never seen or used an earth rod dia larger than 3/4''. Although i'm aware there are quite a few designer type earth electrodes available, but that's another matter!! Secondly while taking soil resistivity readings are an important factor, they are only giving you, if you like the top soil, soil resistivity values. If the ground type changes below, then so will your eventual Ra value. In reality a Topographic survey is also carried out on large or extensive earthing systems. Using a very similar basis to your calculation, i once in the past calculated an earth field, as to how many 2 X 2 rods positions i needed to get somewhere near the Ra value required. Only to find, that after having drilled all these bores, we achieved and surpassed that value with less than 2/3rds of the calculated bore holes. (i've never made that mistake again..lol!!)
The standard bore dia we use is 100mm so you can roughly say that the marconite will increase the rod dia to 100mm. It will also act as the medium of conductivity between the soil medium and the rod, ...No need to wait for consolidation, as the the marconite will fill the bore and to a certain extent, extend into the soil medium itself.
So as i said, if your driving in a few electrodes your not going to gain much by drilling 2 100mm holes and back filling, taking into account cost and time. Just add a little Bentonite as you drive this will help to over come soil consolidation and far less hassle. Your not going to gain much, but then you don't gain that much at 100mm lol.
Again, if talking about domestic, your correct!! But if i were you, i'd save the money your spending on the Bentonite, because that method is a pointless exercise and NO ...it still won't work!! You would find that you wiil achieve far better results by chemical enhancement in the situations you refer too. But ... if you did use bores holes, it would work, and probably work better than your 10% theory too!! lol!!!
Regards Chris
Let's face it, there are cut off points for everything in our industry, you plan/design systems etc, to the requirement of the installation. Same with roded earthing systems, your not going to install a 6m string of magnesium brick anodes to TT a domestic, but you would if you were protecting a very expensive and vital pipe line...
What i will say is, that TT systems today in the UK seems to have become a lost art, along with MICC and other proven wiring methods that now seem to be classed as ''Specialist Only'' lol!!
We could go on and on talking about the various methods, along with there advantages and disadvantages, as TT systems cover a vast area of uses and requirements, depending on it's situation. And that's before considering passive and active Cathodic Protection systems...lol!! So on this one, i think it's better to agree to disagree!! lol!!
Off you go then. But somehow I don't think there will be to many take up on it. Would be interesting though.
HmmJust bumping some threads in the Electrical Wiring Theories and Regulations forum category here on our Electricians Forums. If this specific topic isn't current, just ignore it, it'll drop off the list in no time. However, if it's something you'd like to contribute to, feel free to reply and bring it back into current discussion.