TT system - Reg 411.5.1 | on ElectriciansForums

Discuss TT system - Reg 411.5.1 in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Joined
Nov 30, 2008
Messages
86
Reaction score
4
Just looking at the second part of this reg with the statement " The neutral point or the midpoint of the power supply system shall be earthed. If the neutral point or midpoint is not available or not accessible, a line conductor shall be earthed"
My question is... I assume they are talking about the connection at the transformer sub station and if so why did they feel the need to add this, as I haven't seen it there before now?
 
[ElectriciansForums.net] TT system - Reg 411.5.1

reg 411.5.1 it states every exposed conductive part is provided by a single PPD shall connected ,via the main earthing to the common earth terminal .
 
Hi - yes that is a new sentence in the 18th. Like you, I think they must be referring to the transformer mid point being earthed at origin, as per fig 3.10, which has not changed. Sorry, I’m at a loss why they’ve added it too.
 
Added to add confusion.
 
Just looking at the second part of this reg with the statement " The neutral point or the midpoint of the power supply system shall be earthed. If the neutral point or midpoint is not available or not accessible, a line conductor shall be earthed"
My question is... I assume they are talking about the connection at the transformer sub station and if so why did they feel the need to add this, as I haven't seen it there before now?
This relates to portable generators.
 
I do you know why the a88 holes write the books and put the appendix at the back of the books is beyond me. when you are looking for things ,they has well right it in Chinese. or Arabic .
 
I do you know why the a88 holes write the books and put the appendix at the back of the books is beyond me. when you are looking for things ,they has well right it in Chinese. or Arabic .
It's like trying to read one of your posts Buzz... :D
 

Reply to TT system - Reg 411.5.1 in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
743

Similar threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
782
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top