Just looking at the second part of this reg with the statement " The neutral point or the midpoint of the power supply system shall be earthed. If the neutral point or midpoint is not available or not accessible, a line conductor shall be earthed"
My question is... I assume they are talking about the connection at the transformer sub station and if so why did they feel the need to add this, as I haven't seen it there before now?
 
IT+Earthing+System.jpg

reg 411.5.1 it states every exposed conductive part is provided by a single PPD shall connected ,via the main earthing to the common earth terminal .
 
Hi - yes that is a new sentence in the 18th. Like you, I think they must be referring to the transformer mid point being earthed at origin, as per fig 3.10, which has not changed. Sorry, I’m at a loss why they’ve added it too.
 
Just looking at the second part of this reg with the statement " The neutral point or the midpoint of the power supply system shall be earthed. If the neutral point or midpoint is not available or not accessible, a line conductor shall be earthed"
My question is... I assume they are talking about the connection at the transformer sub station and if so why did they feel the need to add this, as I haven't seen it there before now?
This relates to portable generators.
 
I do you know why the a88 holes write the books and put the appendix at the back of the books is beyond me. when you are looking for things ,they has well right it in Chinese. or Arabic .
 
I do you know why the a88 holes write the books and put the appendix at the back of the books is beyond me. when you are looking for things ,they has well right it in Chinese. or Arabic .
It's like trying to read one of your posts Buzz... :D
 
Thanks for all the replies.... much appreciated!
I fully understand the principles of a TT system, but thanks to those who added anyway, just not the unnecessary insert in the regs and for what reason this is helpful to anyone, to be honest.
 
How would TN-S work if there’s no reference to earth?

If there is no reference to earth, and it is intentionally designed to be this way then it would be IT, It won't be TT.
If there is no reference to earth when they is supposed to be then it will be dangerous.
 
If there is no reference to earth, and it is intentionally designed to be this way then it would be IT, It won't be TT.
If there is no reference to earth when they is supposed to be then it will be dangerous.
Yes, which is why they are saying, reference one of the line conductors to earth.
 
How would TN-S work if there’s no reference to earth?

It's not TT due to the fact that the reference point isn't transferred through the mass of earth. I.e from a rod at a house to the DNO tx.

A generator with a Rod is TN-S as in all intents and purpose it can be treated as a transformer secondary. Albeit with a low potential earth fault current.

You wouldn't rod a genny and then run phases to whatever you were feeding without a CPC just to install a second rod there. (This instance it would be TT)
 
Sorry to resurrect this thread but has the original question ever been answered elsewhere?
 
Just looking at the second part of this reg with the statement " The neutral point or the midpoint of the power supply system shall be earthed. If the neutral point or midpoint is not available or not accessible, a line conductor shall be earthed"
My question is... I assume they are talking about the connection at the transformer sub station and if so why did they feel the need to add this, as I haven't seen it there before now?
Its all part of the wiring regs poking their nose into DNO matters. Just disregard it.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
TT system - Reg 411.5.1
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
25

Thread Tags

Advert

Thread statistics

Created
Paul505,
Last reply from
Julie.,
Replies
25
Views
5,768

Advert

Back
Top