Hi,
Just a quick point on VD.
Reg 525.4, states that a greater voltage drop than stated in table 12A (app12)
(neglecting the motor circuits etc. part of this reg for the purpose of this discussion) may be accepted, provided that it is verified that the voltage variations are within the limits specified in the relevant product standard for the equipment, or in the absence of a product standard, in accordance with the manufacturers instruction.
So maybe the VD may not be so rigid, depending on the manufactures of the lighting, ie. if the lamps are rated at slightly less than the more common 220V-240V, Iam not suggesting trying to bend the rules by any means, but my interpretation of this reg, was it was meant to stop incorrect functioning of equipment, as always common sense applies.
Just a thought
Just a quick point on VD.
Reg 525.4, states that a greater voltage drop than stated in table 12A (app12)
(neglecting the motor circuits etc. part of this reg for the purpose of this discussion) may be accepted, provided that it is verified that the voltage variations are within the limits specified in the relevant product standard for the equipment, or in the absence of a product standard, in accordance with the manufacturers instruction.
So maybe the VD may not be so rigid, depending on the manufactures of the lighting, ie. if the lamps are rated at slightly less than the more common 220V-240V, Iam not suggesting trying to bend the rules by any means, but my interpretation of this reg, was it was meant to stop incorrect functioning of equipment, as always common sense applies.
Just a thought
Last edited: