M

Mpenhallurick

Hi, just looking for someone to confirm my plan is correct for a new installation, power is coming into the building from a 25mm2 single core SWA with armour as the neutral, that goes through 80A main fuse then through the meter. As the earthing is system, would I then need to run tails through an rcd, then through the KMF before heading into the consumer unit through 3 core SWA, if this is all correct. Would my earth from the SWA connect straight onto the earth rod or would it have to go to somewhere else first.

dont do much domestic work so just wanted to clarify this was correct before carrying out work, many thanks
 
What's "all relevant" mean, only asking because if you are a trainee it may be best if you apply for access to the Trainee section, being blase about your qualification doesn't really help us to tailor a response to your question. A sketch of your plans would help as well.
 
If you mean that you have a supply coming in where the supplier has not provided an earth and you need to install a TT earthing arrangement then all circuits will need protection by a residual current device unless you have a sufficiently low R[SUB]A[/SUB] to allow an MCB / fuse protected arrangement.
Since that level of is not easily obtainable it is very likely that you will need to protect the distribution circuit from the meter to the CU with an RCD to ensure that the distribution circuit will disconnect on an earth fault.
So long as the SWA is connected to the earthing system of the installation then the location of that connection will not be critical but it is likely that you will want to provide an MET close to the origin and connect the SWA to that MET.
 

Reply to TT system with kmf in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
774
You would treat it as a TT installation.
2
Replies
29
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top