Nath88
Howdy all.
A friend of mine has recently bought a house and asked me to pop round and do a few tests just for piece of mind everything's ok.
It's a TT system with 30mA split DB
Ze(Ra) - 10.59 with all bonding disconnected
When I got some Zs readings they were all coming up at around the 15 ohm mark
I know All readings are pretty good (under 1667 - regs and 100 - niceic)
but I can't see how there's such a difference between the Ze and Zs
Ze = Zs + R1+R2
i never took any R1+R2 readings but can't see them being that high. Everything looks good n the DB.
Am I missing something obvious??
Cheers