Hello All,

I am a new member with a question i hope you can help me with.

TT System, Ze test with main earth disconnected from earth bar reading = 195 ohms

Zs test on ring main reading = 0.68 ohms..!

Retested Ze but this time connected to the earth bar (main earth not connected to earth bar) = 0.15 ohms...!

Tested again, this time with gas and water bonding disconnected reading again = 0.15 ohms...!!

Question is, can parallel paths bring the value down by this degree or is this potentially a major issue?

Mickeymarrow
 
Hello All,

I am a new member with a question i hope you can help me with.

TT System, Ze test with main earth disconnected from earth bar reading = 195 ohms

Zs test on ring main reading = 0.68 ohms..!

Retested Ze but this time connected to the earth bar (main earth not connected to earth bar) = 0.15 ohms...!

Tested again, this time with gas and water bonding disconnected reading again = 0.15 ohms...!!

Question is, can parallel paths bring the value down by this degree or is this potentially a major issue?

Mickeymarrow


This is absolutely normal on a TT installation, as Wirepuller said, parallel paths nearly always pull the Zs at the DB way down from the Ra value of the earth electrode.
 

Reply to TT System in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
919

Similar threads

Hi Dave thanks for the info I revisited the premises to change a cooker switch and redone the test from the MET with MET disconnected from DB...
Replies
16
Views
1K
On the minor works in the brown book it has Zdb
Replies
3
Views
298

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top